Well 5% drop and 10mm single phase comes to 12.3A over 200m so not far off it!Single socket maybe?
Well 5% drop and 10mm single phase comes to 12.3A over 200m so not far off it!Single socket maybe?
Doubt it could be that, I just did a quick VD calc and 5% is exceeded at a load of 13A over that distance for 10sqmmSingle socket maybe?
Well 5% drop and 10mm single phase comes to 12.3A over 200m so not far off it!
~12A is a lot of LED illumination!I calculated 7.54v at 13A over 200m but at 12.3A it could be slightly under 5%
but either way certainly nowhere near 3% for lighting!
Yikes!And the sand wont be cheap! 200m at 200mm thick (100mm below cable and 100mm over the top) and say 200mm wide trench = 8cu m (8 builder bags worth)!
Agreed but the OP is being a bit coy as to what the cable is being used for. Assuming a mixed load it 'should' still meet 3% guideline if only 1A of lighting!12A is a lot of LED illumination!
Well the regs still say that but really it is a hang-over from the days of filament lamps and their significant voltage/illumination sensitivity.Agreed but the OP is being a bit coy as to what the cable is being used for. Assuming a mixed load it 'should' still meet 3% guideline if only 1A of lighting!
I probably would too which is why I put 'should' in ' ' and guideline, and is justifiable if not filament/discharge lights.Well the regs still say that but really it is a hang-over from the days of filament lamps and their significant voltage/illumination sensitivity.
I personally would be OK with 5% drop on "mixed" if it is LED lighting. Which it almost certainly would be.
I'm not sure I would bother with lowering the supply OCPD, it just has to be able to provide overload & fault protection for the SWA.I would probably aim for 4% though which would limit the OCD to perhaps 10A for 10sqmm!
You've already done the prior planning without our input thankfully10A supply requested to supply comms kit. Not sure what exactly!
Probably a bit excessive but that is what asked for.
Do they need any network cables along with the power? That would be a good reason to use some duct!10A supply requested to supply comms kit. Not sure what exactly!
Probably a bit excessive but that is what asked for.