Gringoking88
So decline the job, the client not wanting the job done properly does not excuse you from complying with the regulations.
Unless you have managed to design this alteration to the circuit in full compliance with the requirements for double or reinforced insulation then you're putting yourself in a very dubious position. I don't see how you can comply with 412.1.3 in a domestic installation.
The alterations or extensions which you make to an existing installation must comply with the current regulations.
Dave,
Thanks for the reply. The downlights will be class 2 and therefor double insulated and I will only be using plastic switches. To be honest I was not sure about this, so called NICEIC technical to clarify and they said that was I was proposing was fine as long as all accessories are class 2.