Hi, I need some advise or help on the following problem.
RCD failed trip test. Failed ramp test. and faield to trip out when Shorted between Earth and bus bar.
I had replaced the RCD with 3 other units, but still would not trip. (ELI 1.17 Ohms)3 lead test L N E and 2 lead test L-E (still no trip).
It did however trip from the supply meter tail side and earth
Power supplied by over head cables into loft to meter.
Replaced batteries to meter just to make sure
Any hep would bemuch appreciated.
 
Hi, I need some advise or help on the following problem.
RCD failed trip test. Failed ramp test. and faield to trip out when Shorted between Earth and bus bar.
I had replaced the RCD with 3 other units, but still would not trip. (ELI 1.17 Ohms)3 lead test L N E and 2 lead test L-E (still no trip).
It did however trip from the supply meter tail side and earth
Power supplied by over head cables into loft to meter.
Replaced batteries to meter just to make sure
Any hep would bemuch appreciated.

Could you clarify?
 
I agree with both previous posts it could very well be something as simple as supply and load tails reversed, keep us posted on how you get on.
 
Hi Guys,
fault turned out to be no earth, although we had an original ELI of 1.17 ohms. When the bonding was disconnected along with the main earth and an ELI taken from the incoming tails and presumed earth conductor the ELI was over 700 ohms.

I take it that the RCD could not "See" any fault as no current or fault was being detected.

Thanks for all your help on this
 

Reply to Puzzling RCD Fault in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock