It's frightening the amount of tenants who can't tell me where the DB is.
Regarding the rcd testing i had an interesting one the other week.
Went to do an eicr turning the power off flicked the mcbs off then pushed the test button on the rcd ....no luck....turned it off and on manually a few times then joy.
Test finished and one socket changed i turned the power back on only for the RCD to trip on the side that id hust changed said socket. Long story short after getting ----ed with myself it wasn't the socket but an extension lead the tenant had plugged in...earth into the neutral and vice versa. Obviously it had never tripped before as it was stuck and needless to say i didnt bother asking if he'd checked it ever...let alone quarterly or 6 monthly
Regarding the rcd testing i had an interesting one the other week.
Went to do an eicr turning the power off flicked the mcbs off then pushed the test button on the rcd ....no luck....turned it off and on manually a few times then joy.
Test finished and one socket changed i turned the power back on only for the RCD to trip on the side that id hust changed said socket. Long story short after getting ----ed with myself it wasn't the socket but an extension lead the tenant had plugged in...earth into the neutral and vice versa. Obviously it had never tripped before as it was stuck and needless to say i didnt bother asking if he'd checked it ever...let alone quarterly or 6 monthly