W
wildgoose
Just clarifying this for a job next week:-
Discussion:
The total earth cable requirement is >10mm2. Equivalent SWA armouring on this cable is 8.42mm but if you add to it the 2.5mm core, then the total csa is 8.42 + 2.5 = 10.92mm. This therefore meets the >10mm2 earth requirement within the same SWA cable assembly.
Question:
In order to satisfy the >10mm earth cable requirement, I have added the swa armouring copper equivalent value with the earth core. I can't see any problem with this. Discussed it with a colleague Spark and he said he would just rather isolate earth and then TT it. Surely my solution is compliant and safer????
Any comments:-
- Supply is to an outhouse containing extraneous parts (Copper water pipes).
- The supply cable is already installed (3core 2.5mm2 SWA PVC).
- There are adaptor boxes at either end of SWA cable which link the armouring and the earth core together.
- The supply end earth, is then linked to the MET via short length of 10mm earth cable.
- The load end earth will be linked via 10mm cable to a small outhouse CCU and the copper pipes also bonded to the same point with 10mm cable.
- This supply meets all other RCD protection requirements.
Discussion:
Question:
Any comments:-