Just clarifying this for a job next week:-

  • Supply is to an outhouse containing extraneous parts (Copper water pipes).
  • The supply cable is already installed (3core 2.5mm2 SWA PVC).
  • There are adaptor boxes at either end of SWA cable which link the armouring and the earth core together.
  • The supply end earth, is then linked to the MET via short length of 10mm earth cable.
  • The load end earth will be linked via 10mm cable to a small outhouse CCU and the copper pipes also bonded to the same point with 10mm cable.
  • This supply meets all other RCD protection requirements.

Discussion:
The total earth cable requirement is >10mm2. Equivalent SWA armouring on this cable is 8.42mm but if you add to it the 2.5mm core, then the total csa is 8.42 + 2.5 = 10.92mm. This therefore meets the >10mm2 earth requirement within the same SWA cable assembly.

Question:
In order to satisfy the >10mm earth cable requirement, I have added the swa armouring copper equivalent value with the earth core. I can't see any problem with this. Discussed it with a colleague Spark and he said he would just rather isolate earth and then TT it. Surely my solution is compliant and safer????

Any comments:-
 
just been to fetch my tin hat. what you could do is as you describe but add an earth rod at the outhouse as well as using the TNC-S. (sits back and awaits the flak).
 
Unless the customer is a tight arse and trying to screw you on cost! Then I think why overspec if it's already compliant?
 
You cannot add the cpc of the cable to the swa. Either, or both must be 10mm, not combined.
Your choice is to run a separate 10mm bond, or isolate and TT it.
 
You cannot add the cpc of the cable to the swa. Either, or both must be 10mm, not combined.
Your choice is to run a separate 10mm bond, or isolate and TT it.

Ok thanks for the good feedback. I've had a thought this morning that might be the case - Doh!!!

When you think about the performance of a TT system in comparision to this solution, you wonder about the wisdom of this regulation.

Also don't the DNO use their multi stranded concentric cabling linked together to make up the CSA ?

Any chance you can point me to the regulation in the BGB, so I can show the client if necessary?
 
You could consider 433.4.2 (BRB) which is discussing unequal current sharing in conductors and could perhaps be applied to the fault current considerations, or in GN8 9.3.4 specifically states that each parallel cpc should be sized individually to take the full fault current.(whether this is true or not is another matter:helmet:!)
 