Discuss quick bonding question in the Australia area at ElectriciansForums.net

C

chopper

went to a job today we were ony swapping a light fitting but noticed the main bonding was ony in 6mm tri rated cable to the gas, the building was a old pub what is going to be used as a train station, quite a big building thought it would need 16mm earth , but lad i was with said cos it was tri rated cable 6mm would probly be fine, we had a look in regs but couldnt find owt, anyone any idea and where can i find it in rergs
 
Not uncomon to find undersized earthing, worth mentioning to the client about it and indicate an inspection is due.
From what you say the pub is closing i guess they won't bother having it done and when its a train station its under different regs to ours so not an issue as was in place for the work you did although possibly undersized but you would not know that unless it was tested first.
 
had a look in regs, it just says 35mm to 50mm neutral requires 10mm cross sectional are, but is normal stranded 10mm cable diffrernt to 10mm tri rated cable, what the lad was saYING is cos its try rated its equalivelent to 18mm cable, never come acroos this and cant find anything in regs,
also what regs does it come under cos they on about making it a train station with offices
 
tnc -s, 25mm 3 phase 35mm n
Minimum size for bonding with PME is 10mm2 copper for current regs (544.1.1). The current carrying capacity of the cable is not considered and so even though you have an additional 6 amps CCC with tri rated cable (which is still less than 10mm2) this will make no difference to the size of bonding required.
As needasparks says let them know but it probably complied when it was built.
 
so what was you (I) in you calculation or what size of fuse =chopper;409781]been told by the audiabatic equation that it complies[/QUOTE]
 
Since the adiabatic equation does not apply to bonding conductors it is difficult to see how it can comply with the adiabatic equation. the main bonding conductors are selected according to the size of the neutral supply.

I would agree that the bonding conductor is probably suitable, but it does not comply with current regulations.
 
Last edited:

Reply to quick bonding question in the Australia area at ElectriciansForums.net

Similar Threads

Curious about supplementary bonding, I have these two 4mm Cables loose and not connected to anything in my parents house. I presume they are for...
Replies
9
Views
2K
Hi all, I would like some advice on a scenario currently at my workplace. I am replacing a Sub main DB and replacing the wiring to sockets/lights...
Replies
17
Views
2K
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
6K
Some friends are setting up a metal workshop inside a shipping container, on site at a commercial building that rents out studios, workshop space...
Replies
9
Views
1K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock