revolt3k

Is this right? Calculating max demand for new CU Ktc Lights 66% 1.51A Front Room Lights .41A Upstairs Lights 2.11A Kitchen Sockets 100% 32A Living Room Sockets 40% 12.8A Upstairs Sockets 40% 12.8A Oven Radiel (2.5mm on a 16Amp breaker) 100% @ 10A Cooker Radiel 24.16 Calculated from 5800W rating - 10A and then 30% of 14.16A + 5A For Socket 19.25A Boiler Radiel (2.5mm on a 16Amp Breaker) 40% of 16A = 6.41 Totals upto 97.29A Does this look right or am i totally off the ball here lol Cheers
 
Lighting - 66% of total current demand for each circuit
Power - 100% of the first ring circuit + 40% of all other circuits
Cooker - 10A + 30% of remaing rated current + 5% if the CCU has a socket outlet
Shower - No diversity allowable
Instantaneous water heater - 100% of largest heater + 100% of second largest + 25% of of any others
Thermostatically controlled water heater - No diversity allowable
Underfloor heating - No diversity allowable

Hope that covers it for you

Chris
 
You seem to have seperated everything ie kitchen lights then room lights if they are on different circuits fair enough diversity is worked out per circuit so if all your downstairs lights are on one circuit then apply the calculations as per my previous post for each circuit.

Chris
 
Yup, There on seperate circuits mate as the kitchen has 11 50W downlighters.

Does 97A seem high even tho i have allowed for diversity? If i added an electric shower later on it would be well over 100A's and the main fuse if only 100A's etc

Would the 97A be the figure that needs recording or would 100A be the figure?

thanks for your help
 
Check your main fuse and see if its 80A or 100A you might need to upgrade. But then you also have to take into account how often will you have every light in the house turned on and every appliance pulling maximum amps. I would suggest never.

Chris
 

Reply to Quick Diversity Question in the Australia area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi, I would appreciate some views on the following issue I have. The Cooker radial in a house has been wired in 2.5mm T&E, to save the expense...
Replies
12
Views
3K
Could somebody put into lamens terms for me what the diversity is on final circuits (sockets) as per table A2 in the OSG. It reads: "100% of...
Replies
56
Views
21K
Doesn't really matter as I have spare capacity and VD well within limits but I have a sub board fed with 10mm SWA.The sub supplies a 32A socket...
Replies
1
Views
1K
The Ghost
T
Hi I am a sparks from the 15th Ed, did 16, 17 and last year 18th. I am out of practice though as have been office based for 12+ years in a...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock