where would i find this in the red book?

The correction factor for cables installed in free air with 70oC thermosetting insulation and an ambient temperature of 50oC is?

any help would be much appreciated,

regards
 
this is wat is confusing me, it says 70oC thermosetting insulation. the tables has "70oC thermoplastic" and "90oC thermosetting" so which one do i look under?

heres another one, too

The correction factor for cables installed in free air with 90oC thermosetting insulation and an ambient temperature of 40oC is

A: 0.76
B: 0.69
c: 0.96
D: 0.86
 
Last edited:
The new table 4B1 is more limited than the old one.

I think the first questioin may have been a typing error - not unusual for C&G).

Your second question doesn't have the right answer - should be 0.91 - again another C&G error, but I think you copied it incorrectly as only one of the 4 answers (0.76) is a possible answer. They will only list 4 figures which you could get from the table.

However, you can get 90deg thermoplastic and 60deg thermosetting which the table doesn't address.

You need to just go on the temperature rating of the cable, not what it's made of.

The rating factor will allow enough current to heat the cable up to its maximum temp.

So if you have a 90deg thermoplastic in an ambient of 70deg then the rating will be 0.58 which will get it to 90deg

P296 gives ratings and factors for 60deg and 90deg flexible cords whether thermoplastic or thermosetting

Mike
 

Reply to Quicky - 2382 question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

According to note 8 of table 4c1 of bs 7671, cables of differing operating temperatures when grouped together, the current rating is to be based...
Replies
4
Views
468
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Doing a cable calc for college and need to know the ambient temperature of this circuit - Supplied from a board inside where the ambient temp is...
Replies
0
Views
760
Calculate the temperature rise in a system consisting of six conductors carrying 1500 amperes each at 132kV, insulated with XLPE, and spanning a...
Replies
2
Views
504
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
522

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock