you turn power OFF!!

Connect one end to Earth Bar and other to your circuit "live" cable then go to furthest point with test meter and connect your leads to L + E to get R1R2 on a radial circuit!

for ring you can disconnect the socket / cu front and croc clip relevant cables to create your Fig of 8 then go round with tester at outlets!
 
I understand how for radials as I do something similar already with a made up fly lead, but I can't get my head round how to use them for 8's on rings!
 
you have a Pack of 4 leads!! and use 2 of them

1 goes on live of one leg and goes to earth on other leg
1 goes on opposing live and goes to earth on first leg

it saves connecting them together with wago or choc block or god forbid twisting them to create continuity!
 
Ah, I thought there was some miraculous way of using these leads without having to wrench the cables out of the terminal bars :o
Cheers :)
 
Sorry to dig an old tread up would this work by clipping one end to the earth bar and one to the bus bar and turning all the breakers off apart form the one you are testing the R1 + R2 test on? Like shown in the picture on test meter.co.uk? Cheers
 
Sorry to dig an old tread up would this work by clipping one end to the earth bar and one to the bus bar and turning all the breakers off apart form the one you are testing the R1 + R2 test on? Like shown in the picture on test meter.co.uk? Cheers

That would work for radials mate. IMO quickest way to test. Not the procedure for a ring main test
 
Sorry to dig an old tread up would this work by clipping one end to the earth bar and one to the bus bar and turning all the breakers off apart form the one you are testing the R1 + R2 test on? Like shown in the picture on test meter.co.uk? Cheers

Absolutely yes it would.

The only consideration to be given is thaat the internal resistance of the MCB may add to the reading slightly. Sometimes the internal resistance of these devices is higher than we think, particularly if there is an issue with it.

At least testing this way would highlight the issue, before we get to the Zs measurement.
 