L LlandrilloSpark Feb 13, 2013 #16 Like tel says clamp the earth, and pull fuses or switch mcb's to find the leaky circuit
S somersetsparks Feb 13, 2013 #17 almost all wylex and crabtree rcbo's I have ever tested trip between 19 and 23ma even when new
C capitolltd Feb 13, 2013 #18 You need to perform a core balance test to establish the leakage, using a milli ohm clamp meter. If you clamped the earth, the readings would not be correct due to many parallel earth paths.
You need to perform a core balance test to establish the leakage, using a milli ohm clamp meter. If you clamped the earth, the readings would not be correct due to many parallel earth paths.
G Guest111 Feb 13, 2013 #19 Heating pumps usually give a low reading when hot if they are going down,IR when cold and again when hot and see the difference.
Heating pumps usually give a low reading when hot if they are going down,IR when cold and again when hot and see the difference.
E Engineer54 Feb 14, 2013 #20 telectrix said: needs to be a earth leakage clamp meter with a resolution down to at least 1mA Click to expand... Needs to be a lot better resolution than 1mA, at the very least 0.1mA and better 0.01mA!!
telectrix said: needs to be a earth leakage clamp meter with a resolution down to at least 1mA Click to expand... Needs to be a lot better resolution than 1mA, at the very least 0.1mA and better 0.01mA!!