When carrying out a ramp test on an MEM 30mA rated RCD device it trips at 21mA which I think is a bit too low. The customer has an intermittant tripping problem that we think is linked to the heating system because when the tripping becomes a bit more frequent on occassions isolating the heating system is the only way to turn the RCD back on, then the tripping nuisance vanishes again. We have checked the system, carried out insulation tests at 500v on the under ground cabling (as the oil fired boiler is in the garage) and all reading are fine. Would/could the RCD tripping at 21mA be the reason or part of it maybe? Thoughts please.

The incoming system is a TT and the earth electrode measures 19.5 Ohms. The RCD device is about 20/25 years old I would say.
 
Yer that can, and probably is the cause. 27 is healthy imo.

Obviouslly could be an underlying problem with the heating system but i'd definitley change the RCD first.
 
for what an RCD costs, i'd swap it out, then try a ramp test.
 
including the neutrals. there could be some cumulative leakage.
 
I did a half rated test and it held which is good but didn't disconnect any loads (including neutrals) as there's not a lot there being on a sub board. Could it be the same sort of scenario as mass leakage in a computer suite maybe, high integrity earthing etc???
 
The British Standard allow the device to be set anywhere between 16-30mA for a 30mA device. So the device is satisfactory and meets that standard. If the device tripped at 15mA or below, the device would not, hence the 1/2 rated test.
I suggest you use a clamp meter to establish we're the leakage current is originating.
 
The British Standard allow the device to be set anywhere between 16-30mA for a 30mA device. So the device is satisfactory and meets that standard. If the device tripped at 15mA or below, the device would not, hence the 1/2 rated test.
I suggest you use a clamp meter to establish we're the leakage current is originating.

Ok thank you all for the response I'll try then clamp meter approach next and take it from there.
 
needs to be a earth leakage clamp meter with a resolution down to at least 1mA
 
I had a job not long back with a crabtree 30mA RCCB tripping during the night. Ramp test showed the RCD tripping at 21mA. Replaced it with a new one and they've not had a problem since.
 
needs to be a earth leakage clamp meter with a resolution down to at least 1mA

That might present a problem as mine doesn't do mA let alone go down to 1mA :(

I'll beg,borrow or steal one, well maybe not steal

Thanks for the info very much appreaiated.
 
You could by 10 RCDs from the manufacturer, same model, type, ratings, yet they all differ slightly from 16-30mA, hence why changing the RCD can work. But you may be masking a problem. Lets not forget the dangers of earth leakage.
No problem, always here to help
 
You could by 10 RCDs from the manufacturer, same model, type, ratings, yet they all differ slightly from 16-30mA, hence why changing the RCD can work. But you may be masking a problem. Lets not forget the dangers of earth leakage.
No problem, always here to help


Not keen on changing the RCD as I've been down that road in the past and sometimes it does the trick other times not, so it's a lottery and yes earth leakage can be dangerous so for now we have to keep on looking.
 