When carrying out a ramp test on an MEM 30mA rated RCD device it trips at 21mA which I think is a bit too low. The customer has an intermittant tripping problem that we think is linked to the heating system because when the tripping becomes a bit more frequent on occassions isolating the heating system is the only way to turn the RCD back on, then the tripping nuisance vanishes again. We have checked the system, carried out insulation tests at 500v on the under ground cabling (as the oil fired boiler is in the garage) and all reading are fine. Would/could the RCD tripping at 21mA be the reason or part of it maybe? Thoughts please.
The incoming system is a TT and the earth electrode measures 19.5 Ohms. The RCD device is about 20/25 years old I would say.