Yes, it's standard with protection equipment for the higher voltages or for very large or important lv installations (eg Southampton air traffic control centre - some years ago now!).
Although ramp testing is not the thing to do.
You usually test straight forward overcurrent equipment at 2x, 5x and 10x, in addition if it has instantaneous trip (which mcbs do) 1.2x that value. (and adjust the 10x down if needs be)
Basically you prove the characteristic trip curve.
If you are testing protection relays, these have a rating of 1 or 5A, so 30x could be 30 or 150A
The standard unit I use is a sverker - which is 100A (and includes timer etc)
Alternative is a pte from smc
For higher currents or primary injection testing, I use a CSU - which is good for 600A
If you need more than this an ingvar does around 2000A
The most common ones do tend to be megger, but smc, abb, cee and many others make kit that can do it.