Hi to everyone, I'm new on the forum and a almost a new in this world too. I got my full qualifications done in April but never done any job yet.
So I'll try to explain the situation in the best way I can

3 double light holder on the outside of a wall are on a single way switch. The switch is on a 6 way gang for other inside light.
All the floor light are on B20 RDC, all the fuse board has been changed 5 years ago on 17th edition.

The problem become when, randomly, the lights outside are on and the RCD trips. Doesn't seem to be any particular time/load that let the RCD to trip. Can be all the lights on together or that one outside only on and the RCD trips. But not every time does happen. Same time happen once a day a some time 15.
I checked if the lights holder are in short somehow. Line and CPC are insulated correctly from each other. All the 6 bulbs are brand new and all correctly working too.
I tried to bypass the cable between the switch and the lights with a flying cable. No difference.
Tried to leave one bulb at time but no difference, still tripping.
Does anybody have any idea about it.
THANK YOU ALL
 
Btw the cables are 5 years old. They don't carry more than 300W and I don't think they get degraded so quickly with so little load. They are 2 and E 1,5mm between the holders and the switch and 2 and E 2.5 to the MB.
Just my opinion.
 
Last edited by a moderator:
You say that you have dried lights with a hair drier,
I would be amazed if this fault has nothing to do with water ingress.
The fact you have dried them suggests they were wet.
Also, could there be a junction box somewhere full of water?
 
You say that you have dried lights with a hair drier,
I would be amazed if this fault has nothing to do with water ingress.
The fact you have dried them suggests they were wet.
Also, could there be a junction box somewhere full of water?
I use the hair dryer to dry out some potential moisture. No sign of water in.
Also no junction box. Straight from the switch to the holder. Each holder is connected to each other in parallel with the straight connectors, that I also changed with a brand new wago 221 ( I guess)
 
If you can disconnect 2 of the lights
L+N you will be able to see if the fault lies between the switch and 1st light or the other 2 lights
I did disconnected all of them and turn it on one at time with a brand new 2and E as flying cable straight from the switch. Is a really irritating situation. Also because people around are thinking that I'm trying my luck guessing something
 
I think the best plan is to wait for your tester to arrive. Do you have an experienced electrician that you can consult?
 
Hi - if RCD only trips when the lights are on, then it’s likely there is some fault there. You’ve not seen a fault yet and as others have said you’ll need your tester (borrow one?).

Two thoughts in the meantime -
It is possible for a wonky switch that has contact bounce to trip an RCD, but you would always see that at switch on or off and it’s pretty rare.
As the RCD tripping is almost random, it may be the RCD is finally tripping due to added leakage from something else being used, kettle is a classic suspect :) .
 

Reply to Random RCD's tripping in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
424
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
372
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
2K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
514
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock