Got a job where another electrician was supposed to do an EICR, but spotted a couple of cables that were eaten by rodents and switched the power off, telling the tenants that it was dangerous and a fire hazard.

His testing didn't yield any results, or none he put on the EICR, just a couple of C1s for cable damage and non ip rated spots in shower.

Anyway, had a good look round and done some insurance resistance tests, and although some readings are a bit low, around 5Mohm, and found some damage where rats have eaten outer insulation. Only in 2 places have they gone through to copper, and these have been repaired previously with insulation tape.

The board is on a TT supply, with 100mA up front doing 6 circuits and 30mA protecting other 6 circuits.

I am trying to work out the best thing to do - most cables are totally inaccessible being a converted barn with vaulted ceilings - where the cables are accessible there is only 2 majorly damaged cables.

What would your next move be? Obviously landlord has been told about the risk of arcing and fire but I think there's very little chance of that happening.

Anyone had similar problems?
 
just fill your eicr in and give it to the customer yes 5meg ohm is a bit low but still a pass recomend it needs improvement and cover yourself in the limitations table
 
Got a job where another electrician was supposed to do an EICR, but spotted a couple of cables that were eaten by rodents and switched the power off, telling the tenants that it was dangerous and a fire hazard.

His testing didn't yield any results, or none he put on the EICR, just a couple of C1s for cable damage and non ip rated spots in shower.

Anyway, had a good look round and done some insurance resistance tests, and although some readings are a bit low, around 5Mohm, and found some damage where rats have eaten outer insulation. Only in 2 places have they gone through to copper, and these have been repaired previously with insulation tape.

The board is on a TT supply, with 100mA up front doing 6 circuits and 30mA protecting other 6 circuits.

I am trying to work out the best thing to do - most cables are totally inaccessible being a converted barn with vaulted ceilings - where the cables are accessible there is only 2 majorly damaged cables.

What would your next move be? Obviously landlord has been told about the risk of arcing and fire but I think there's very little chance of that happening.

Anyone had similar problems?
I had to smile when I read that bit.
 
Had similar on a marina install rats using cable duct to jetty as a runway had chewed thru most insulation on 50mm supply singles not much we could do recommend replacement, IR was fine so client not too bothered just poured about 4 ton of poison In there
 
So an EICR with no test results and just observations - not work the paper its printed on then!
 
Well that's what I told the landlord - they were there 5 hours and the test results are all N/A, even the characteristics of supply are totally wrong, as are the circuits and their descriptions. They may as well have been testing nextdoor for all I know.

Also the photos attached to the report has 4 out of 7 pictures of TV coax cables that have been chewed, plus an armoured which was very slightly knawed!! Well if they can go through steel I will be damned....
 