Folks.
I need to install a defib unit outside on a wall.
Does this require an RCBO or not, just wondering as the unit has a small heater within and should it trip out for any reason other than under fault conditions (it is in a dampish environment, a harbour) it will get damp.
So MCB or RCBO.
Many thanks
AJ.
 
All the same regulations apply as they do to any other circuit.

Go through the list of reasons why RCD protection may be required and if none of them apply then it is not required.
 
The link mentions RCD protection at note 10...

But the 4A (time-lag) fuse spur seems a bit strange. Why not a regular 3A?
 
Just a thought and probably not relevant but there are some exceptions in the regs regarding medical equipment,
cant remember exactly what they are but on occasions protection may be omitted or reduced to ensure the device remains functional.
or am I thinking of lifting magnets? its been a long day but there are a few things to look up in the bible if any one is interested.
 
The power required is not for medical equipment… it’s for a light and a heater.

The defib itself is self contained battery powered.
 
Me thinks this is being over thought. As @davesparks suggests in #5 this is the correct method to follow. Something which may get damp needs to be installed to prevent this and not compensate by fitting an RCD which is not a solution.
 
I'm aware of 3 defibs local to me that have been vandalised over the years, doors kicked off etc, leaving the heaters and guts exposed, so whenever i do them i have an rcd.
 