I ICE Jun 26, 2009 #1 what is the operating current of an RCD used to provide ADS on a domestic TT installation with an earth electrode resistance of 150 ohm? Is it a trick question?
what is the operating current of an RCD used to provide ADS on a domestic TT installation with an earth electrode resistance of 150 ohm? Is it a trick question?
S securityvillage Jun 26, 2009 #2 No you use 50 divided by RA(150) = I delta n Hope that helps Upvote 0
G Guest123 Jun 26, 2009 #3 Hey. I would say 30mA regardless of the RA as on TT the max disconnection time for an instantaneous trip i.e 5 x iDN = 150mA, is 0.2s. Upvote 0