I've had a customer contact me stating their RCD operates at 0030 every night and they are unable to reset it until about 0730 in the morning.
I've yet to go investigate.
I've suggested disconnecting/isolating any equipment that may have a timer built in but this doesn't clear the issue.
Any suggestions that could make my life easier? Besides carrying out obvious RCD tests. Cheers
off peak sounds a likely culprit. is the immersion on a timer?
beat me to it, sounds like something on Economy 7 that's switching on, or not as it might be.
Is there an immersion heater in use , could be the E7 controller with maybe a faulty immersion element , They probably use central heating for the hot water along with the immersion and probably don't realise its coming on at night and is part of the old E7 heating setup ,just a thought like,,,,
Do they have gas ch?
If so what time is the clock set for (off periods).
Pump fault when cold, boiler overrun changeover fault, cylinder stat wet when not being heated??? etc etc.
Just thinking aloud. (hmm, reminds me, Girls Aloud!)
Boydy
The RCD affected is from the original domestic supply c/u.
Not the redundant off peak supply.
Have now tested RCD which is fine and searched for any timed appliances that may cause this. None.
Customer has informed me that this fault only occurred since bad storms a couple weeks ago following a 17 hr power cut. I'm now assuming this is a distributor problem?
How many circuits are protected by this RCD?
How many appliances/points are "served" by the circuits?
What are the IR readings for these circuits?
Have you read post 8 yet , Re the immersion heater , usually fed from the general supply and probably got a timer on it ,,,,