Sbc

Hello to all the good people on this forum... Just letting you all know I passed my Napit assessment today so am over the moon, however I'm a little disappointed to find that Napit don't recognize the Logic part p certificate but hey, never mind, anyway a quick query if I may...

Im about to fit a security light into a rewirable fuse board, 5 amp, the manufacturers instructions say it "should be 30mA RCD protected", however the method of installation im going to use will fall outside of the regs requirement for RCD protection so do i follow manufacturers instructions or regs?

Thanks to all in advance.
Steve
 
as above. even when stupid, follow their instructions. wire it from a RCD FCU.
 
I would use my judgement. The manufacturer is just trying to cover themselves to the maximum by recommending RCD protection. The word "should" is not the same as "must". There's no requirement for RCD protection of outside lighting unless needed for a TT supply or if the cables are buried <50mm in the structure.

If the light is readily accessible to people, especially children, then I might add RCD protection. If it's out of reach, and only accessible to someone doing repairs or maintenance, I probably wouldn't force the additional cost of an RCD on the customer.

Maybe I need to get the tin hat out?
 
Defined scope Levels B & C Assessment 17th edition, Full scope electrical level A - 17th edition and PIR. I couldn't believe it when the assessor told me... apparently I need to go and get assessed at there office by taking another 80 question exam and a 7 hour practical the following day, pretty much exactly the same as I've already done... has anyone else had problems?
 
Presumably there is a charge for this "service"?
If you meet their minimum requirements for membership tell them to do one. If you don't meet their minimums then they should not have come out to assess you.
 
Was always under the impression that any external lighting thats fixed to the building didn't need RCDing, but the cables supplying it may do.

Might be wrong, will have a butchers through regs later
 
Theres no charge for this service, I think i have to do it within 12 months. Its just a pain cause ive done once and i have to lose time from work to do it again.

Training courses are selling the fact that you can join a competent person scheme with this certificate... check out this link Logic Part P Domestic Installer | Part P Training Course.

Anyway Im just happy to be a full member.

Regarding the RCD, internal cable will be in trunking and it not TT so no rcd requirement according to regs. it can be installed at 1.5m-2m so i guess its because its accessable to people as handyspark said, and the manufacturer is just covering themselves.

Thanks to all for advise, Steve
 
510.3 "Every item of equipment shall be selected and erected so as to allow compliance with the reulations stated in this chapter and the relevant regulations in other parts of BS7671 and shall take account of the manufacturers' instructions."
 
[h=2]Install electrical installations in domestic properties[/h]Introduced in 2005, Part P covers the safety and compliance of electrical installations in domestic properties. After completion of this Part P course, learners are able to register on to a competent person scheme such as Gas Safe, Elecsa, NICEIC, or NAPIT.


Safe, Elecsa, NICEIC, or NAPIT.
Suitable for:

Tradesmen who need to carry out and certify electrical work in domestic dwellings such as

  • Kitchen fitters and joiners
  • Heating engineers and plumbers
  • Electricians
  • And Electrical Engineers.



Retrain from scratch:

This course is a core module in both of our training course packages, designed to retrain anyone to become a Domestic Electrical Installer.


Well if it's designed to train engineers it must be the course to end all courses
 
"...and shall take account of the manufacturers' instructions."

Quite. Which means you can't ignore them but it also means that you don't have to slavishly follow them to the letter either. A good electrician will be able to use his judgement and knowledge of the regulations to do a safe and cost-effective installation in a whole variety of situations.
 