Hello to all the good people on this forum... Just letting you all know I passed my Napit assessment today so am over the moon, however I'm a little disappointed to find that Napit don't recognize the Logic part p certificate but hey, never mind, anyway a quick query if I may...
Im about to fit a security light into a rewirable fuse board, 5 amp, the manufacturers instructions say it "should be 30mA RCD protected", however the method of installation im going to use will fall outside of the regs requirement for RCD protection so do i follow manufacturers instructions or regs?
Thanks to all in advance.
Steve
Im about to fit a security light into a rewirable fuse board, 5 amp, the manufacturers instructions say it "should be 30mA RCD protected", however the method of installation im going to use will fall outside of the regs requirement for RCD protection so do i follow manufacturers instructions or regs?