neutral and earth are already connected upsteam (at least in england anyway and i imagine else where as well).i cant think of any upstream fault that would affect an (RCD) Residual Current Device .
a downstream neutral to cpc fault will only trip an (RCD) Residual Current Device if a circuit with at least double the actual tripping current (maybe more due to unequal cable sizes) is powered on.this could be as little as 40mA (assuming a 20mA actual trip current)
a downstream neutral to cpc fault will only trip an (RCD) Residual Current Device if a circuit with at least double the actual tripping current (maybe more due to unequal cable sizes) is powered on.this could be as little as 40mA (assuming a 20mA actual trip current)