Bit of a tricky situation this one. I got called out to an apartment complex that had had a big flood, the top flat had a major leak and it went right through the 5 floors on one side of the building, I was surprised but apparently its a timber building with no real fire breaks between floors apart form some doubled up plaster boarding.

They moved all the tenants out on that side of the building and got me in to disconnect all the circuits in the various apartments, test them all and just leave one socket circuit on if I could for the dehumidifiers, which I did. They wanted and EICR on each flat because they are very concerned about potential fire spread once the rotten plasterboard is removed being a timber framed building.

Now these apartments were build about 20-25 years ago, they are wired in brown/blue but don't have any RCD protection at all, they are just a straight isolator board full of MCB's (13 in each flat). No supp bonding from what I can see in the bathrooms, (I'm sure you had to bond the lights/heater supply etc to the pipe work if no RCD's were present back in 2002 or so). I also found various other more minor things wrong in a few flats.

Due to the fact they were so paranoid about the risk of fire in a wooden building I put a price in to change all the boards, 5 of them for RCBO type but it got knocked back and they don't want it doing. I think it was the insurance company that knocked this work back, understandably as they are there to pay for the damage, not bring the apartments up to spec. But where do we go from here, I know there is no likelihood of the sockets being used outdoors as per the regs at the time but I have to re-connect all the circuits back into the board and I cant do this if the bonding isn't present in the bathrooms. can I cross bond the lights/pipework/downflow in 2026 and say it complies with the regs today so no RCD needed? Or do I just say tough, new boards needed and its not my problem.

Just to add, I don't want to "bend" the rules so they get their way, I had a nice little earner out of this so its by the book or not at all.
 
Your work must comply with current Regulations so avoiding additional RCD protection is not going to be workable.
 
No, I thought that, in one apartment, I physically disconnected every live and neutral in the consumer unit but I thought this will be an absolute nightmare to connect back up if the unit isn't changed. So in the others I just removed the bus bar and neutral link and wired a temp supply to a few sockets for the dehumidifiers. Does putting the bus bar and neutral link back in constitute "work" to current regulations? Thing is I'm guessing for the handover they will want a cert to say everything is up to the latest standards for "fire safety" and then it will become my problem if it isn't. Do I just say it needs a new board no exceptions before the power is restored and I don't care who pays for it.
 
I thought you were changing the boards regardless. Taking out and refitting a busbar doesn't really constitute anything. If they want the old boards left in situ just carry out EICRs noting any departures from current regulations.
 
My neighbour had a flood a few years ago, and I replaced everything but the cable and brought it up to current spec.

Any old devices such as MCBs may have dampness issues and could now be faulty.
Original metal back boxes became rusty, even if not apparent straight away.

Also brought the number of smoke detectors up to whatever the current regs at the time.

There was no arguments from insurance company.


You can’t just “put it back to how it was”



I wouldn’t be happy leaving it as was.

I also would think your temporary sockets for dehumidifiers need to be rcd protected as well.
That has been a new installation and needs to follow today’s regs. However temporary it is.
 
I thought you were changing the boards regardless. Taking out and refitting a busbar doesn't really constitute anything. If they want the old boards left in situ just carry out EICRs noting any departures from current regulations.
Only if I get paid to change them, I suppose its no different to disconnecting a ring final to test it and then re-connecting it back to the MCB, technically you have powered up a non RCD socket circuit but you are only putting it back how it was 5 minutes ago.

It was more the lack of bonding in the bathrooms if there isn't any RCD protection, the bathrooms for the flats are all on top of each other and that is mainly where the leak was so everything in the bathrooms will be renewed like the light, fan and downflow, all the wiring is staying as it will be fine once its dried out. Can we still run a piece of 4mm bond to the light and heater and say it doesn't need an RCD or would you just say we are changing like for like so it doesn't matter.

Also the job is 60 miles away and I think they are going to start re-bording quite soon so I won't be able to run any bonds in anyway when I go back. Up to now I've only been asked to do the reports and make safe.
 
Putting supplementary bonding in place does not eliminate the requirement for additional RCD protection in the flats.
 