Bit of a tricky situation this one. I got called out to an apartment complex that had had a big flood, the top flat had a major leak and it went right through the 5 floors on one side of the building, I was surprised but apparently its a timber building with no real fire breaks between floors apart form some doubled up plaster boarding.
They moved all the tenants out on that side of the building and got me in to disconnect all the circuits in the various apartments, test them all and just leave one socket circuit on if I could for the dehumidifiers, which I did. They wanted and EICR on each flat because they are very concerned about potential fire spread once the rotten plasterboard is removed being a timber framed building.
Now these apartments were build about 20-25 years ago, they are wired in brown/blue but don't have any RCD protection at all, they are just a straight isolator board full of MCB's (13 in each flat). No supp bonding from what I can see in the bathrooms, (I'm sure you had to bond the lights/heater supply etc to the pipe work if no RCD's were present back in 2002 or so). I also found various other more minor things wrong in a few flats.
Due to the fact they were so paranoid about the risk of fire in a wooden building I put a price in to change all the boards, 5 of them for RCBO type but it got knocked back and they don't want it doing. I think it was the insurance company that knocked this work back, understandably as they are there to pay for the damage, not bring the apartments up to spec. But where do we go from here, I know there is no likelihood of the sockets being used outdoors as per the regs at the time but I have to re-connect all the circuits back into the board and I cant do this if the bonding isn't present in the bathrooms. can I cross bond the lights/pipework/downflow in 2026 and say it complies with the regs today so no RCD needed? Or do I just say tough, new boards needed and its not my problem.
Just to add, I don't want to "bend" the rules so they get their way, I had a nice little earner out of this so its by the book or not at all.
They moved all the tenants out on that side of the building and got me in to disconnect all the circuits in the various apartments, test them all and just leave one socket circuit on if I could for the dehumidifiers, which I did. They wanted and EICR on each flat because they are very concerned about potential fire spread once the rotten plasterboard is removed being a timber framed building.
Now these apartments were build about 20-25 years ago, they are wired in brown/blue but don't have any RCD protection at all, they are just a straight isolator board full of MCB's (13 in each flat). No supp bonding from what I can see in the bathrooms, (I'm sure you had to bond the lights/heater supply etc to the pipe work if no RCD's were present back in 2002 or so). I also found various other more minor things wrong in a few flats.
Due to the fact they were so paranoid about the risk of fire in a wooden building I put a price in to change all the boards, 5 of them for RCBO type but it got knocked back and they don't want it doing. I think it was the insurance company that knocked this work back, understandably as they are there to pay for the damage, not bring the apartments up to spec. But where do we go from here, I know there is no likelihood of the sockets being used outdoors as per the regs at the time but I have to re-connect all the circuits back into the board and I cant do this if the bonding isn't present in the bathrooms. can I cross bond the lights/pipework/downflow in 2026 and say it complies with the regs today so no RCD needed? Or do I just say tough, new boards needed and its not my problem.
Just to add, I don't want to "bend" the rules so they get their way, I had a nice little earner out of this so its by the book or not at all.