Evening all,

Was in a school carrying out RCD testing recently and the way we were going about it was - going to the DB finding the circuit and going to the position of the circuit (Mostly sockets in classrooms) and carrying out the RCD testing there, By the time we read through the circuit charts, found the location of the points on that circuit, confirmed these points were infact on that circuit and then the old x1/2, x1 and x5 all both at 0 and 180 degrees it took some time.

The main problem was the classroom locations have mostly been renamed since the circuit charts were provided. However the question is, later on we were carrying out work in another school and there was another company in carrying out rcd testing - He just stood at the DB and went down all the RCBOs and tested them at the L + N terminals of the RCBO and he said you could test an RCD at any point in the circuit is this correct? It saved him hours of labour time for searching for classrooms and the exact positions of the points on that circuit.

Thanks :smile5:
 
Hmm interesting, thanks for that Archy, is there anything in the regulations stating that? Thanks
 
It is acceptable to confirm the RCD tripping times for compliance at the terminals of the device. However, unless you know exactly what the device in question is actually protecting it is strongly advised that this is investigated and verified. Accurate circuit schedules and labelling is a requirement of BS7671.
 
Thanks for confirming that rattlehead, I know about the requirement of up to date circuit charts they have been informed of that and will soon be corrected when remedial works of there Periodic inspection
 
still a damn sight easier to plug in the MFT, whack it on auto, then just flip the RCD back on 4 times.
 
It is acceptable to confirm the RCD tripping times for compliance at the terminals of the device. However, unless you know exactly what the device in question is actually protecting it is strongly advised that this is investigated and verified. Accurate circuit schedules and labelling is a requirement of BS7671.
aye but surely on an ECR (i`m assuming thats what this was)...you would`v identified which subs/finals the OPDs/RCDs/RCBOs served before just diving in....
 
It is acceptable to confirm the RCD tripping times for compliance at the terminals of the device. However, unless you know exactly what the device in question is actually protecting it is strongly advised that this is investigated and verified. Accurate circuit schedules and labelling is a requirement of BS7671.


Think you have that the wrong way round!! You test RCD devices at the CU/DB with the circuit disconnected for recordable confirmation (or otherwise) purposes. But is acceptable to conduct an RCD test downstream for say other purposes. As RCD tests come way down the line in the order of testing procedures, circuit identification should have been well and truly sorted and verified long before the RCD tests are conducted....
 
Think you have that the wrong way round!! You test RCD devices at the CU/DB with the circuit disconnected for recordable confirmation (or otherwise) purposes. But is acceptable to conduct an RCD test downstream for say other purposes. As RCD tests come way down the line in the order of testing procedures, circuit identification should have been well and truly sorted and verified long before the RCD tests are conducted....

I would agree, on an eicr its the last test I do, right after meggering, tin hat on
 