O.S.G. : Polarity
( Dead ) ... Before the supply is connected ... ( By continuity methods’ )
( Live ) ... With the supply connected and energized ... re-check of polarity, using an approved voltage indicator .
Polarity (Regulation 612.6) .. ( By continuity methods )
it is important to confirm that :
i) overcurrent devices and single-pole controls are connected in the line conductor only .
iii ) Socket-outlet(s) & similar accessory polarities are correct .
O.S.G. After connection of the supply , polarity must be checked using an approved ( Voltage indicator or a test-lamp ) in either case with fused leads - GS-38 .
Polarity checks must be carried out on all circuit’s , i.e. Power & Lighting .
Testing checklist O.S.G .
Polarity : this includes checks that single-pole control and protective devices .. switches , circuit-breakers , fuses , are connected in the line conductor only .
Polarity : Neutral conductor and that wiring has been correctly connected to socket-outlets and other accessories .
GN-3 : 612.6. Polarity testing
The polarity of all circuits must be verified before connection to the supply, with either an ohmmeter or the continuity range of an insulation & continuity tester
( Simplicity ) Alternative , polarity can be verified by visually checking core colours at terminations, thus verifying the installer’s connections .
Whatever method is used, polarity checks are required at all points on a circuit.
Just back for my Torque screwdriver . off to the wholesaler now , Pen to Paper , Why ??
Once again, the “ powers that be " The argument on both sides
Some Questions am asking myself ?? (( Manufacturers or Electrician’s ))
Fires have been caused by loose connection(s) We will never hear to end of this .
The most common cause the Neutral not being tightened correctly. On rant mode here .
Just back from a job , to replace down lights to LED . the costumer asked the question, the RCDs keeps tripping why ?? had a look inside the CCU , did hear an arking inside the CCU connection, “ reason “ due to a loose connection, Tail / Neutral
it was the smell of something burning . that got my Attention .
( Start with N ) An Installer replaced a CCU 4 weeks ago, to my dismay the ( Tail ) Neutral was not tightened up making me (( loose connection )
signs of Heavy blacking on the main-switch 100A ( N ) made safe at the moment , going to the wholesaler to get a replacement MK main-switch 100A.
The question the customer asked , Who do I take it up with the ( N****C / Installer ) Yeah , dam right .
This poor person is a pensioner
My gripe .
The way manufacturers make the (( terminals )) It’s a starting point !!
So, in particular, under Amendment 3 enclosures will need to be made from a suitable non-combustible material, or be enclosed in a cabinet / enclosure made from a suitable non-combustible material complying with regulation 132.12.
it's high time the bigwigs listened to the contractor(s). Electricians’
Where does it stop, Socket-outlets , ceiling roses , junction boxes , IP plastic enclosures !!
DNO service cut out so will this need to be incased in a suitable enclosure ( is it fireproof plastic / combustible material)
Something should be done regarding meter tails or the way manufacturers make the (( terminals ))
How many times have you tightened the tails half way through a consumer unit , only to find they are lose again at the end of the job , so who is at fault here .. The way manufacturers make the (( terminals )) Question(s) have to be asked here !!
( A3) Chapter 42 Protection Against Thermal Effects
Regulation 421.1.200 has been introduced and will require switchgear assemblies, including consumer units, to have their enclosure manufactured from non-combustible, or not readily combustible, material, or to be enclosed in a cabinet or enclosure that is constructed of non-combustible, or not readily combustible, material.
This new Regulation is being introduced to help to protect against fire that can result from the overheating of connections within consumer units. Overheating can arise from loose connections and connections that have not been made correctly, for example, the connection of a cable over the insulation.
Regulation 421.1.200. This regulation requires that within domestic (household) premises, consumer units and similar switchgear assemblies shall comply with BS EN 61439-3 and shall have their enclosure manufactured from non-combustible material, or enclosed in a cabinet or enclosure constructed of non-combustible material and complying with Regulation 132.12. This has been developed to safeguard against the risk of fire that can be produced from the overheating of connections in consumer units.
Reactions: 1 person
Chapter 41 Protection Against Electric Shock References to ‘ordinary persons’ in Regulation 411.3.3 have now been removed.
This Regulation will require, in accordance with Regulation 415.1, RCD protection for socket outlets up to 20 A (and for mobile equipment up to 32 A for use outdoors) for all installations.
There is, however, an exception for RCD protection (for socket outlets up to 20A) for a specific labelled socket outlet or where a documented risk assessment determines that RCD protection is not necessary.
This means that socket outlets up to 20A in all types of installations, including commercial, domestic and industrial, will need to be protected by a 30mA RCD unless a risk assessment can determine that it’s not necessary
Reactions: 1 person
Part 2 Definitions: For example, the definition for ‘skilled and instructed persons’ will be changed. It was also decided that the definition for a ‘competent person’ should be removed, to avoid confusion, as it was considered that some overlap existed between the definition of ‘skilled person’ and ‘competent person’
These changes will be reflected throughout the wiring regulations. For example, Regulation 134.1.1 has been changed from:
"Good workmanship by competent persons or persons under their supervision and proper materials shall be used in the erection of the electrical installation. Electrical equipment shall be installed in accordance with the instructions provided by the manufacturer of the equipment." to: "Good workmanship by skilled (electrically) or instructed (electrically) persons and proper materials shall be used in the erection of the electrical installation. The installation of electrical equipment shall take account of manufacturers’ instructions." Some new symbols have been included in the definitions.
Reactions: 1 person
When connecting single-phase loads to a three-phase supply, you must take care to distribute the single-phase loads equally across the three-phases so that each phase carries approximately the same current .
Q) This is called:
a) generation of the phase loads
b) transmission of the load
c) distribution of the load
d) balancing of the load
Balancing single-phase loads
A three-phase load such as a motor has equally balanced phases since the résistance of each phase winding will be the same , Therefore , the current taken by each phase will be equal. when conning single-phase loads to a three-phase supply , to distribute the single-phase loads equally across the three-phases so that each phase carries approximately the same current . equally distributing the single-phase loads across the three-phase supply is known as “ Balancing the load
The metal structural steelwork of a building is called:
a) the general mass of earth
b) the circuit protective conductor ( CPC )
c) exposed conductive parts
d) extraneous conductive parts
What is Main Protective Bonding ? .. The question is the purpose of Equipotential Bonding
Main protective equipotential bonding connects the main earthing terminal with the following extraneous-conductive-parts
Exposed metallic structural parts of the building .. connecting all accessible metalwork
Equipotential bonding :
Electrical connection which maintaining various exposed-conductive-parts & extraneous-conductive-parts at substantially the same potential .
Extraneous-conductive-parts – this is the structural steelwork of a building
Q&As
To verify or prove a successful electrical isolation you would use a:
a) voltage indicator
b) voltage proving unit
c) set of GS-38 test leads
d) small padlock
To secure an electrical isolation you would use a:
d) small padlock
Where a test instrument or voltage indicator is used to prove a supply dead, the same device must be tested to show that it still works using a:
d) small padlock
To give adequate protection to the person carrying out a safe isolation procedure, the test instrument must incorporate a:
d) small padlock
Hazard may be defined as: ( A3 - 2015 ) reminds us Risk Assessment comes into the Equation now .
- Anything that can cause harm
- the change , large or small , of harm actually being done .
Magnetic circuit through core . Vp ) the primary voltage .. 230V
Magnetic circuit through core . Vs ) the secondary voltage .. 12V
Np ) the number of primary turns .. 800
Ns ) the number of secondary turns
moving the terms around you have a general expression for a transformer: Vp - Vs = Np - Ns
230V to 12V emergency transformer is constructed with 800 turns , Calculate the number of ( Ns ) secondary turns required
Ns = Np Vs / Vp , therefore Ns = 800 x 12V ÷ 230 = 42 turns rounded up . 41.739 13043
( A3 - 2015 ) Skilled Person :
Inspection & Test , Part 6 chapter 61 , change to “ Skilled person ( electrically ) “ being competent in inspection , testing , and certification
Skill wise you will need to be an effective communicator with strong interpersonal skills with an analytical brain as you will need knowledge and experience and continuous improvement. skilled person
(( competent person )) now replaced with skilled electrically
Physics
" You can throw all the philosophy you like at the problem, but at the end of the day it's just basic electrical theory !"
Electrical résistance
Electric current is the flow of electrons through a conductor , When the electrons move from one part of the conductor to the other , they collide with other electrons and with the positive ions present in the conductor , Due to these collisions , there is some obstruction or opposition to the flow of electronic current through the conductor . These collisions tend to slow down the speed of the electrons .. ( + / - )
The property of a conductor by virtue of which it opposes the flow of electric current through it is called its résistance.
Factors affecting the résistance of a conductor
The electrical résistance of a conductor ( cable / wire ) depends on the following factors
length of the conductor
Area of cross-section of the conductor ( thickness of the conductor )
Temperature of the conductor
Material of the conductor ..
Copper have very low résistance
Effect of the length on the résistance of a conductor
On increasing the length of ( cable / wire ) its résistance increases and on decreasing the length of the ( cable / wire ) its résistance decreases
In other words ; the résistance of a conductor is :
Shorter ( cable ) wire .. lower résistance
Longer ( cable ) wire .. higher résistance
Directly proportional to it length ( R / I )
R = résistance
I = length
• if the length of the conductor ( Cable ) is doubled , its résistance also gets doubled
• if the length of the conductor ( Cable ) is halved , its résistance also gets halved .
Effect of the area of cross-section on the résistance of a conductor
The résistance of a conductor is inversely proportional to is area of cross-section
if the area of cross-section of the conductor is doubled , its résistance gets halved .
if the area of cross-section of the conductor is halved , its résistance gets doubled .
The potential difference is measured by an instrument your ( megger ) is always connected in parallel to the two-points across which the potential difference is to be ( measured ) . Little ( rS )
Cable ( wire ) Measuring the potential difference between two-points ( A to B ) by using your megger .. little ( r[SUP]1[/SUP] ) to ( r[SUP]1[/SUP] ) Loop , Continuity
(( Continuity )) of ring-final-circuit (( conductor(s)
Note : Little ( rS )
Step 1 ) Check between each (( end )) in turn
Line-to-line ( r[SUP]1[/SUP] )
Neutral-to- Neutral ( r[SUP] N[/SUP] )
Circuit-protective-conductor to circuit-protective-conductor ( r[SUP]2[/SUP] )
Unit of résistance
SI unit of résistance is Ohms , which is denoted by the symbol Ω .
According to Ohms law
Résistance ( R ) = Potential difference ( V ) ----- Current ( I )
Now , if the potential difference ( V ) is 1 volt &
The current ( I ) is 1 ampere
Then the résistance ( R ) in the above equation will be 1Ω
1 ohm = 1 volt ----- 1 ampere or 1Ω = 1V --- 1A
1 ohm is the résistance of a conductor such that when a potential difference of ( 1V ) is applied to its ends , a current of ( 1A) flows through it
( r[SUP]1[/SUP] & R[SUP]1[/SUP] ) r[SUP]1[/SUP] , r[SUP]2[/SUP] & r[SUP]N[/SUP] are the end-to-end ring-final-circuits readings .
R[SUP]1 [/SUP]) is the maximum measured résistance of the line-conductor for a circuit .
R[SUP]2 [/SUP]) is the maximum measured résistance of the circuit-protective-conductor for a circuit .
( R[SUP]1[/SUP] + R[SUP]2[/SUP] ) is the test reading value of the two résistance added together
:rant: On rant mode , regulation 421.200
100A disconnector(s) are a higher risk of overheating they carry a heavier load . (( why not improve them )) Manufactures
Main isolation disconnectors with just one-terminal screw for a 25mm[SUP]2[/SUP] cable (( cause for concern ))
We used them in the past , 2 screw terminals used for 100A ( Switches ) disconnectors , cooker switches
Has regulation 421.200 been influenced by fire safety alone !
Are plastic consumer units being blamed for other types of electrical fires !
One aspect of an installation that is rarely upgraded ( except in extreme cases ) is the electricity supply intake equipment on the DNO side of the meter
Many of the cables , connections and cut-outs have been in place and rarely touched since they were first installed up to 60 years . plus
(1) The safe isolation procedure .. ( You isolate to Stop )
(( Before starting ))
(2) remember to seek permission from a relevant responsible person , because there might be certain vital services that must not be interrupted at any time , There might be a permit to work system in place to which you will need to comply .
(3) Identify the point of isolation for the system or circuit , lock-off , place warning label , keep the key to the lock with yourself .
(4) Select the correct and mains approved test equipment , ensure that it works correctly by testing on the proving unit .
(5) Test the outgoing side of the means of isolation (( Main switch , circuit-breaker , fuse )) etc to make sure it is dead , (( Depending on the type of supply )) you will need to complete the following tests .
(6) Single-phase installations test to confirm that there is no voltage between :- Line and Neutral , Line and Earth , Neutral and Earth .
(7) Phase installations test to confirm that there is no voltage between , L1 & L2 , L1 & L3 , L1 and Neutral , L1 and Earth , L2 and L3 , L2 and Neutral , L2 and Earth , L3 and Neutral , L3 and Earth , Neutral and Earth .
(8) Re-test the test equipment on the proving unit .
(9) When isolating the main source of energy it is also essential to isolate any secondary sources such as ( standby generators , uninterruptible power supplies ( UPS ) and microgenerators )
Step 1 .
• Identify the point of isolation for the system or circuit . ( Electricity takes the path of least résistance )
• Lock off. ( Prevention )
• Place warning label (( Warning Electrician Working & Do Not Switch On ))
• Keep the key to the lock with yourself.
Step 2 .
• Select the correct and main approved test equipment .
• Ensure that it works correctly by testing on the proving unit.
Step 3 .
Objectives • Test the outgoing side of the mean of isolation ( Main switch , Circuit-breaker Fuse ) To make sure it is Dead .
• Depending on the type of the supply you will need to complete the following tests:
• Single-phase installations test to confirm that there is no voltage between :
Line & Neutral
Line & Earth
Neutral & Earth
• Three-phase installations test to confirm that there is no voltage between :
L1 & L2
L1 & L3
L1 & Neutral
L1 & Earth
L2 & L3
L2 & Neutral
L2 & Earth
L3 & Neutral
L3 & Earth
Neutral & Earth
Step 4 .
2394 your Q/As Safe isolation . When isolating the main source of energy it is also essential to isolate any (( Secondary sources )) such as :
- Standby generators . refer (9)
Re-cap “ The human body is a conductor “
Electricity must have a complete path . You only get one change to prove (( Safe Isolation )) Electricity flows through Conductors . Water , Metal . The Human body .
Circuit-breakers provided to protect Equipment not people .
Fuses , are designed for self destruction , under fault conditions .
Reactions: 1 person
As a Skilled person, Firstly this is a template for learning curve , Excises only . What Codes , are appropriate . ?? & recommendations’
No answers will be given “ As an Inspector “
Observation
Regulation 612.10. RCD does not operate in the required time
612.1. Unable to gain access to carry out all tests. Due to the condition and/or method of installation of the electrical equipment the inspector cannot be confident that it is safe for continued use, therefore further investigation is recommended
612.1. Unable to shut-down due to client operational limitations to carry out all tests. it is the inspector’s opinion that there is no apparent risk for continued use and therefore, as agreed with the client that this observation is categorized as a limitation ( Limit ) subject to safe isolation procedures are put in place before any maintenance on electrical equipment is carried out .
612.3.2. Low insulation résistance reading(s) recorded
612.9. Unable to shut-down due to client operational limitations to carry out earth-loop-tests , readings entered are from carrying out an ( r[SUP]2 [/SUP] ) test only , with a wandering lead fed from another live source to prove earth-continuity , therefore , unable to ascertain whether the earth-loop-impedance is low enough to operate the protective device in the required time . it is the inspectors opinion that there is no apparent risk for continued use and therefore, as agreed with the client , this observation is categorized as a limitation ( Limit ) subject to safe isolation procedures are put in place before any maintenance on electrical equipment is carried out .
612.9. Unable to gain access to carry out earth-loop-tests , readings entered are from carrying out an ( r[SUP]2 [/SUP] ) test only , with a wandering lead fed from another live source to prove earth-continuity , therefore , unable to ascertain whether the earth-loop-impedance is low enough to operate the protective device in the required time . it is the inspectors opinion that there is no apparent risk for continued use and therefore, as agreed with the client , this observation is categorized as a limitation ( Limit ) subject to safe isolation procedures are put in place before any maintenance on electrical equipment is carried out .
Regulations 612. Protective device(s) removed, unable to carry out live tests
612. Testing .
Regulation 612.6. Unable to gain access to confirm whether polarity is correct , Due to the condition of the electrical equipment and/or method of installation the inspector cannot be confident that it is safe for continued use , therefore further investigation is recommended
Regulation 612.6. Unable to shut-down due to client operational limitations to confirm whether polarity is correct , it is the inspector’s opinion that there is no apparent risk for continued use and therefore , ( As Agreed with the Client ) This observation is categorized as a limitation ( Lim ) subject to safe isolation procedures are in place before any maintenance on electrical equipment is carried out .
Regulation 612.3.1. Unable to gain access to carry out insulation résistance test(s) Due to the condition of the electrical equipment and/or method of installation the inspector carrying out this inspection cannot be confident that it is safe for continued use, therefore further investigation is recommended
Regulation 612.3.1. Unable to carry out insulation résistance test(s) due to risk to (( Electronic components on the circuit )) it is the inspectors’ opinion that there is no apparent risk for continued use and therefore , as ( Agreed with the Client ) this observation is categorized as a limitation ( Lim )
Regulation 612.2.1. & 612.9. Unable to gain access to confirm whether the protective conductor is ( Continuous throughout circuit(s) Due to the conditions of the electrical equipment and/or method of installation the inspector cannot be (( Confident that it is safe for continued Use )) therefore further investigation is recommended
Regulation 612.2.1. & 612.9. Unable to shut-down due to ( Client ) operational limitations to confirm whether the protective-conductor is continuous throughout circuit(s) therefore unable to carry out an earth-loop-impedance test(s) it is the inspectors’ opinion that is no apparent risk for continued use and therefore, as (( Agreed with the Client )) this observation is categorized as a limitation ( LIM ) subject to safe isolation procedures’ are in place before any maintenance on electrical equipment is carried out .
Regulation 612.9. Unable to gain access to carry out earth-loop tests . Due to the condition of the electrical equipment and/or method of installation the inspector cannot be confident that it is safe for continued use, therefore further investigation is recommended
Regulation 612.9. Unable to shut-down due to client operational limitations to carry out earth-loop tests, it is the inspectors’ opinion that there is no apparent risk for continued use and therefore, as agreed with the client , this observation is categorized as a limitation ( LIM ) ) subject to safe isolation procedures’ are in place before any maintenance on electrical equipment is carried out .
My own Option
You don't put a round peg in a square hole, however it would seem no one taught the manufacturers ? ( CCU ) 25mm[SUP]2[/SUP] Tails
Periodic Inspection & Testing . You.re Q , is it fit for Continuous Use .
Re-cap , Scope : GN-3
it is essential that the inspector and the person ordering the inspection agree the extent of the installation to be inspected beforehand, and any criteria regarding the limit of the inspection. The details should be recorded on the Certificate .
Regulation 612.8.1. Unable to gain access to verify all details of the protective device. Due to the condition of the electrical equipment and/or method of installation the inspector cannot be confident that it is safe for continued use, therefore further investigation is recommended
Regulation 612.8.1. Unable to shut-down to client operational limitations to gain access to verify all details of the protective device. it is the inspectors’ opinion that there is no apparent risk for continued use and therefore, as agreed with the client, this observation is categorized as a limitation ( LIM )
Regulation 612.2.2.
(( Continuity )) A test shall be made to (( Verify the continuity of each conductor )) including the protective-conductor, of every ring final circuit .
Regulation 612.2.2.
Continuity reading high on ring-final-circuit ( R[SUP]2[/SUP] ) suspect loose termination or broken ring-connection . You.re call As a Inspector
Regulation 612.2.2.
Regulation 612.2.2.
Continuity reading high on ring-final-circuit ( R[SUP]2[/SUP] ) suspect loose termination or broken ring-connection . You.re call , As a Inspector
514.9.1. Circuit(s) description missing / no circuit chart , unable to trace circuit(s) therefore unable to carry out test(s)
514.9.1. Circuit(s) description incorrect , unable to trace circuit|(s) therefore unable to carry out test(s)
612.8.1. Details of the protective device missing or not visible , therefore unable to test for compliance ?
612.1. Unable to gain access to carry out full testing due to the presence of ( Asbestos ) Due to the condition of the electrical equipment and/or method of installation the inspector cannot be confident that it is safe for continued use, therefore further investigation is recommended .
612.1. Unable to shut-down due to client operational limitations to carry all tests, it is the inspectors’ opinion that there is no apparent risk and therefore, as agreed with the client , this observation is categorized as a limitation ( LIM ) subject to safe isolation procedures are in place before any maintenance on electrical equipment is carried out .
Unable to gain access to verify type and size of (( DNO fuse )) 612.1.
612.6. Polarity incorrect .
612.10. RCBO does not operate in the required time .
612.10. Time delay on RCBO operating in a time exceeding the setting of the device .
415.1.1. Where an RCBO has been installed and is used for additional-protection the RCBO failed to operate at less or equal to 40mS at a residual current of 5 IΔn