O.S.G. : Polarity
( Dead ) ... Before the supply is connected ... ( By continuity methods’ )
( Live ) ... With the supply connected and energized ... re-check of polarity, using an approved voltage indicator .
Polarity (Regulation 612.6) .. ( By continuity methods )
it is important to confirm that :
i) overcurrent devices and single-pole controls are connected in the line conductor only .
iii ) Socket-outlet(s) & similar accessory polarities are correct .
O.S.G. After connection of the supply , polarity must be checked using an approved ( Voltage indicator or a test-lamp ) in either case with fused leads - GS-38 .
Polarity checks must be carried out on all circuit’s , i.e. Power & Lighting .
Testing checklist O.S.G .
Polarity : this includes checks that single-pole control and protective devices .. switches , circuit-breakers , fuses , are connected in the line conductor only .
Polarity : Neutral conductor and that wiring has been correctly connected to socket-outlets and other accessories .
GN-3 : 612.6. Polarity testing
The polarity of all circuits must be verified before connection to the supply, with either an ohmmeter or the continuity range of an insulation & continuity tester
( Simplicity ) Alternative , polarity can be verified by visually checking core colours at terminations, thus verifying the installer’s connections .
Whatever method is used, polarity checks are required at all points on a circuit.
( Dead ) ... Before the supply is connected ... ( By continuity methods’ )
( Live ) ... With the supply connected and energized ... re-check of polarity, using an approved voltage indicator .
Polarity (Regulation 612.6) .. ( By continuity methods )
it is important to confirm that :
i) overcurrent devices and single-pole controls are connected in the line conductor only .
iii ) Socket-outlet(s) & similar accessory polarities are correct .
O.S.G. After connection of the supply , polarity must be checked using an approved ( Voltage indicator or a test-lamp ) in either case with fused leads - GS-38 .
Polarity checks must be carried out on all circuit’s , i.e. Power & Lighting .
Testing checklist O.S.G .
Polarity : this includes checks that single-pole control and protective devices .. switches , circuit-breakers , fuses , are connected in the line conductor only .
Polarity : Neutral conductor and that wiring has been correctly connected to socket-outlets and other accessories .
GN-3 : 612.6. Polarity testing
The polarity of all circuits must be verified before connection to the supply, with either an ohmmeter or the continuity range of an insulation & continuity tester
( Simplicity ) Alternative , polarity can be verified by visually checking core colours at terminations, thus verifying the installer’s connections .
Whatever method is used, polarity checks are required at all points on a circuit.