pmslhave you stabbed it through the neutral of the supply cable?
I've always put at least two rods on a TT mate as it was how I was taught but this time I'd gotten the first one in and got about 180/90 coupled another knocked that in and took 100 ohms off that then I thought oooo how low can you go so whacked the third in, read 0.29 and thought I'll stick there. Gaffer wasn't happy at first when he spotted all his shiny new rods had gone but when he saw my test sheet I had yet another convert
Just the difference between 3/8" rod and 5/8" rod is a lot though isn't it, I can't believe how many people just stick in 3/8" rod, I have only used these for temporary stakes for genny's and cabins.
Hell yeah mate I won't use those little bloody twigs, I've seen them used a million times and then heard"Oh that'll be fine".Just the difference between 3/8" rod and 5/8" rod is a lot though isn't it, I can't believe how many people just stick in 3/8" rod, I have only used these for temporary stakes for genny's and cabins.
yes the armouring is earthed but it is glanded to a seperate metal clad box, not the metal clad fuse board. Sorry I didnt make this clear.