I can cut a hole in the wood boad maybe. Thank you I will make it accessible

I still don't think thats acceptable unless you make it big enough to be able to use spanners to check the tightness of the SWA gland

I would have run the SWA up to the bottom of the CU and glanded it directly to it - less parts, accessible .
 
Last edited by a moderator:
Rear entry, no problem, done it many times, also side entry. The top and bottom gland plates run out of room very fast . Does the building not have any steelwork to bond ?
 
There is no issue with the wooden board and there is no issue with a rear entry tho. It all conforms to BS7671

I didn't question the rear entry, just the large size of it and the combustible material it's sat on. Potential fire containment is surely a consideration when choosing installation methods regardless of whether it's acceptable in BS7671?
 
Sorry to be nitpicking - just trying to help. The swa that's concealed behind the wooden board - as the armour has been removed it now needs RCD protection (?).
 
Hi,

Is it OK to create a rear entry in an eight way three phase BD.

Please see photo attached.

A technician friend of mine says he has never seen this done before?

View attachment 43904

There is no issue with creating an entry as you describe. Although I do think it could be done a bit better than the way it has been done in the photo.
 
To be constructive, a much better solution would be to

A) use the 3phase meter kit that Wylex make for this board that fits neatly inside utilizing the front bottom left knockout for the screen.

B) gland that armoured straight into the bottom.

C) If you wish cables to enter the rear a id drill a few 50mm holes rather than 1 huge one as sealing up is going to be untidy, you dont want a mouse in there!, i recently fitted one of these boards and went for rear entry for the swa incomer, but i could walk down an access behind the board so glanded in the rear properly
 
I wouldn’t really worry about the back board being flammable, it’s probably less so than the plastic DB.
Not sure what the small CSA conductors are for?
 
I would have brought the cables into a bit of 100x100 trunking below the DB, removed the plate at the bottom of the board and taken the cables up through a slot in the top of the trunking protected by a bit of paxolin or even rubber edging, maybe even grommet strip :eek:
I'd have glanded the SWA into the bottom of the trunking.
 
I hope these photo's will answer some of the questions (also open me up to some abuse)
If anything needs changing I will change it.

40233515_238741993503726_953987999664701440_n.jpg

40081957_232647510755422_2855882720439959552_n.jpg

40139729_419263751931135_5804280823142154240_n.jpg

40081957_232647510755422_2855882720439959552_n.jpg

40143923_231184077561517_1506995610601914368_n.jpg

40198834_2191658291118894_1852597468403859456_n.jpg

40136606_2009656472405831_5819611541401501696_n.jpg

39753191_258615154768665_624772575968362496_n.jpg

40203210_341280623110261_6921439668378533888_n.jpg

40143923_231184077561517_1506995610601914368_n.jpg
 
Why could the meter not be at the supply end?

This is a secondary board. This is a private meter just for this building. Mains supply branches off to 5 buildings, each with a private meter so the landlord can meter each building separately
 