I i=p/u Nov 19, 2013 #1 What reference method isit for t&e or yy cable in basket then dropping down stud wall....? Thx if you can help
What reference method isit for t&e or yy cable in basket then dropping down stud wall....? Thx if you can help
I i=p/u Nov 19, 2013 #3 Suppose so Andy. Worst case is it runs in 50mm of insulation in the drops. But not sandwiched .No books to hand
Suppose so Andy. Worst case is it runs in 50mm of insulation in the drops. But not sandwiched .No books to hand
A Andy78 Nov 19, 2013 #4 I only have my OSG, so A if in conduit within the wall, 102 if the cable is against the plasterboard, 103 if it's enclosed in insulation. That's for T+E obviously.
I only have my OSG, so A if in conduit within the wall, 102 if the cable is against the plasterboard, 103 if it's enclosed in insulation. That's for T+E obviously.
I i=p/u Nov 19, 2013 #5 Il write in 102 , soundsgoodenough , thought would if been a b c d e or f .. Thx
A Andy78 Nov 19, 2013 #6 http://www.electriciansforums.co.uk/inspection-testing-certification-electrical-installations/70017-reference-method-explained.html