What reference method isit for t&e or yy cable in basket then dropping down stud wall....?

Thx if you can help
 
Suppose so Andy.

Worst case is it runs in 50mm of insulation in the drops. But not sandwiched .No books to hand
 
I only have my OSG, so A if in conduit within the wall, 102 if the cable is against the plasterboard, 103 if it's enclosed in insulation. That's for T+E obviously.
 
http://www.electriciansforums.co.uk/inspection-testing-certification-electrical-installations/70017-reference-method-explained.html
 