Discuss Regs Confusion in the Australia area at ElectriciansForums.net
I
irishsailor
Am I correct in thinking that you do not need to mechanical protect cables in walls, (Lighting & Power circuits) if they are kept within the zones??
However if you go outside the zones
you need mechanical protection
unless it is at a depth of 50mm
RCD protected
plus others
Please Advise??
Regards
Hey mate.
Cables buried in walls less than 50mm wether they are in a prescribed zone or not need 30mA RCD protection or can be run in earthed metallic conduit without RCD protection.
They must have one of the two above froms of protection.
Cheers.
Hi Irishsailor
You are correct but you still have to take into account the conditions likely to be encountered, not much in domestic though. sheathing is good practice but not a requirement.
Regards
Lenny's right
In a domestic situation, even cables in prescribed zones need to be at least 50mm deep or earthed armoured or in earthed conduit/trunking or mechanicaly protected.
Or if none of the above they must be protected by a 30ma RCD.
Reply to Regs Confusion in the Australia area at ElectriciansForums.net
hello, i am just about to completely rewire a refurbished house. i have done the same to several houses in the distant past. i have just read...
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
I had a PV system installed by a local reputable manufacturer last autumn; since then, I've received conflicting advice regarding the consumer...