Discuss Relationship ze and pfc in the UK Electrical Forum area at ElectriciansForums.net
So I’m currently studying Ze and pfc etc kind of understanding it.
main question really is about the relationship between them both I understand that the lower the Ze the higher the fault current but why is this? Is it just simply to do with ohms law? And I’m just over thinking and confusing myself
Any responses would be appreciated
A lower loop impedance allows more current to flow, and yes this is Ohms law.
Think of what happens when each variable is changed, either up or down. Example - what would happen to the PFC figure if the supply voltage was higher?
For a single phase domestic supply, where Ze/Zs is dominated by the cable resistance, it is just Ohm's law:
PFC = U / Ze
Typically your MFT reports both the PFC and Ze when measured, the PFC is based on the measured voltage U, but Ze is independent of that. You would use Ze along with R1+R2 (or Zs at the end of a circuit) to check that any over-current protection will disconnect fast enough for safety even at the lowest likely supply voltage.
The worst case PFC (of both earth-fault 'PEFC' and supply short-circuit 'PSCC' ) would be used to check that any over-current protection is able to safely interrupt any fault.
For three-phase and/or high current systems it gets more complicated, but the same basic principles apply. The IET's "Electrical Installation Design Guide" has some examples of the slightly more tricky cases on pages 76-81
It's a long time since I was at school, but isn't I = V/R the same as V = IR something like transposing one of the divisors to the other side of the resultant make it a multiplicand rather than a divisor?
It is indeed. I think they were joking though.
I think it buried in the Multiverse with Jean Luc Picard. ? If anyone is confused it's a joke.
I find my sense of humour is directly proportional to the amount of wine I have drunk, I'm a giggler not a fighter. ?
Reply to Relationship ze and pfc in the UK Electrical Forum area at ElectriciansForums.net
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Hi there, firstly wishing you all good health and happiness 🙂 Just a few questions if you all don’t mind answering for me please.. I’ve just...
OLDBOY
O
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...