So I’m currently studying Ze and pfc etc kind of understanding it.
main question really is about the relationship between them both I understand that the lower the Ze the higher the fault current but why is this? Is it just simply to do with ohms law? And I’m just over thinking and confusing myself

Any responses would be appreciated
 
So I’m currently studying Ze and pfc etc kind of understanding it.
main question really is about the relationship between them both I understand that the lower the Ze the higher the fault current but why is this? Is it just simply to do with ohms law? And I’m just over thinking and confusing myself

Any responses would be appreciated

A lower loop impedance allows more current to flow, and yes this is Ohms law.

Think of what happens when each variable is changed, either up or down. Example - what would happen to the PFC figure if the supply voltage was higher?
 
For a single phase domestic supply, where Ze/Zs is dominated by the cable resistance, it is just Ohm's law:

PFC = U / Ze

Typically your MFT reports both the PFC and Ze when measured, the PFC is based on the measured voltage U, but Ze is independent of that. You would use Ze along with R1+R2 (or Zs at the end of a circuit) to check that any over-current protection will disconnect fast enough for safety even at the lowest likely supply voltage.

The worst case PFC (of both earth-fault 'PEFC' and supply short-circuit 'PSCC' ) would be used to check that any over-current protection is able to safely interrupt any fault.

For three-phase and/or high current systems it gets more complicated, but the same basic principles apply. The IET's "Electrical Installation Design Guide" has some examples of the slightly more tricky cases on pages 76-81
 
It's a long time since I was at school, but isn't I = V/R the same as V = IR something like transposing one of the divisors to the other side of the resultant make it a multiplicand rather than a divisor?
 
It's a long time since I was at school, but isn't I = V/R the same as V = IR something like transposing one of the divisors to the other side of the resultant make it a multiplicand rather than a divisor?

It is indeed. I think they were joking though.
 
I think it buried in the Multiverse with Jean Luc Picard. ? If anyone is confused it's a joke.

I find my sense of humour is directly proportional to the amount of wine I have drunk, I'm a giggler not a fighter. ?
 

Reply to Relationship ze and pfc in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
953
Hi there, firstly wishing you all good health and happiness 🙂 Just a few questions if you all don’t mind answering for me please.. I’ve just...
Replies
1
Views
565
OLDBOY
O
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
679

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock