The RMT230 was installed by the boiler technician and has the following connections:
  • neutral to 4
  • live to 1
  • boiler wire to 2 (what I take to be NC, "normally closed")

1000006200.png
However, there's no timer function, so I got a TP5001M off eBay, and I want to wire it myself because we're skint.

Here are the presumed mappings, if you could please correct me if I'm wrong:

  • neutral to N
  • live duplicated with a 3way WAGO to L and COM
  • boiler wire to NC

(I guess 2nd live is isolated so as to power the display and timer electronics.)

Thanks, and I wish everyone a merry Xmas.

1000006199.jpg

Doc links:
RMT 230: https://assets.danfoss.com/documents/355544/AN000086406038en-000102.pdf
TP5001M: https://assets.danfoss.com/documents/356364/AN30483462054701-000102.pdf
 
I think your mapping is correct.

The relay contacts on your new thermostat are 'volt free' to give the unit more flexibility, so they can be used to switch any control circuit, be it mains or low voltage etc.

Your proposal with the Wago is fine, but I might just put a short wire link between L and COM, as the L terminal should accommodate 2 x 1.5mm, or whatever you have!
 
I think your mapping is correct.

The relay contacts on your new thermostat are 'volt free' to give the unit more flexibility, so they can be used to switch any control circuit, be it mains or low voltage etc.

Your proposal with the Wago is fine, but I might just put a short wire link between L and COM, as the L terminal should accommodate 2 x 1.5mm, or whatever you have!
Shorting L and COM is genius, and no need for a wago.

Thanks for the reply 🙏
 
Shorting L and COM is genius, and no need for a wago.

Thanks for the reply 🙏
I missed the fact that your switched live to the boiler should go to the NO contact, not NC.
Sorry! 🫣

Difference between a passive thermostat and an electronic one!
 
I missed the fact that your switched live to the boiler should go to the NO contact, not NC.
Sorry! 🫣

Difference between a passive thermostat and an electronic one!
On the RMT230's SPDT diagram, the (1)-to-(2) closed path shows the temperature going down, which tells me (2) is the NC point, hence my assumption that the boiler wire should go to the equivalent point on the TP5001M.

I'll try your suggestion of NO first, but just check that the worst case scenario is that the heating works backwards, right? 😅
 
I'll try your suggestion of NO first, but just check that the worst case scenario is that the heating works backwards, right? 😅
Correct. No harm will be done either way !
Your references to NO and NC are correct.

My take is that the 'mechanical' RMT 230 is a bimetallic strip, where the NC contact is closed (at cool temp). As the temp increases, the strip bends, and eventually the contact snaps to the other NO side, which turns off the boiler. So in that situation NC is the one to use. That premise is supported by the diagrams, as you say.

With the new thermostat, the NO and NC contacts are in a relay activated by the electronics. Here the terminology refers to the 'normal' unpowered state of the relay.
So with the thermostat unpowered. The relay NO contacts are open.
When you turn the thermostat on, assuming programmer is not calling for heat, the NO contacts stay open. It's not until the programmer /thermostat power the relay (ie call for heat) that the NO contacts close.
With the electronic version, it's the NO contacts that close to demand heat. It's the other way round with the bimetallic strip.
 