I need to do the customer a report on this. done buy a supposed "electrician" via Bathroom installers. This SWA is for a 9.5kW shower.

apart from the SWA armour not being earthed, the black core is used as cpc but no Gn/Y ID. joins in loftto T/E in a broken adaptable box with 30A 3 pole choc strip. the SWA is exposed in the CU room and drilled out through cavity wall, then takes a convoluted route up outside wall to attic. Apart from having 2 tight bends where it enters wall, it's a bloody eyesore. a minor point is the grey conductor is unused and I beleive it should be connected to earth.

They have at least fitted a 40 RCBO albeit a Wylex in an Ashley& Rock CU.

What i need is reg. nos. from 18th for above non-compliances if anyone could oblige, as I still only have 17th (3rd Amdt.)joannaCU.jpg
 
Last edited by a moderator:
not got mine to hand but you are going to get a lot of reg numbers thrown at you by many I suspect.

reg 155.TH155.5H1T.4.RE4L
springs to mind??
 
526.1 Every connection between conductors or between a conductor and other equipment shall provide durable electrical continuity and adequate mechanical strength and protection. Broken box and 30A choc block no good for that.
[automerge]1587036297[/automerge]
Most of section 134 Erection and Initial Verification.

134.1.1 Good workmanship by skilled or instructed person. Proper materials to be used in the errection of the electrical installation. The instalation shall take into account manufacturers' instructions.
 
Last edited:
my draft report.
Report on Shower installation



!. SWA cable does not have the steel armour earthed.

2.The SWA is not adequately supported at the Consumer Unit ( 522.8.5 )

3. The black conductor used as cpc is not identified as such (Green/Yellow Sleeving or tape required)

4. The joint in the attic to Twin&Earth cable is inadequately joined with 30A connector blocks, as the circuit load is 41A. There is no strain relief provided. ( 526.1. & 522.6 )

5. The RCBO fitted is 40A. This is inadequate as it does not comply with Ib<In<Iz.

6. Where the SWA enters the structure, the bend radii are too tight ( Reg. 522.8.3 )

7. The SWA cleats outside are spaced too far apart ( Reg. 522.8.4. )

Section 134 of BS7671 applies.

It is my considered opinion that this installation is non-compliant; the SWA outside the building will allow water ingress into the masonry and is an eyesore.

My recommendation is to rip it out and start again.
 
Armour not earthed, 411.3.1.1
Conductor identification, 514.3
Unsuitable connection enclosure, 526.7
Bends in swa cable, 522.8.3
Non compatible protective device, 536.4.203
There are multiple Regs you could throw at this including the slick termination of the cable at the board.
 
Armour not earthed, 411.3.1.1
Conductor identification, 514.3
Unsuitable connection enclosure, 526.7
Bends in swa cable, 522.8.3
Non compatible protective device, 536.4.203
There are multiple Regs you could throw at this including the slick termination of the cable at the board.
SUPER. THANK YOU.
 
I wouldn’t include no 5 in your report, as overloaded protection can be omitted for fixed loads such as a shower so ib<In<Iz is not relevant, you just need to make sure that the Iz of the cable is large enough including the protective device for the load of the shower and that you have the required fault protection.
So in this case the rcbo is incorrectly sized for the final load 433.1.1 (i)
 
Last edited:
well, it doesa work. but can't for the life of me understand fitting an instantaneous shower when it would be far less work fitting a mixer shower, hot feed from C/H boiler. all the necessary pipework( not necessarily in the right order though) is under the floor only about 4 ft. away.
[automerge]1587049839[/automerge]
I wouldn’t include no 5 in your report, as overloaded protection can be omitted for fixed loads such as a shower so ib<In<Iz is not relevant, you just need to make sure that the Iz of the cable is large enough including the protective device for the load of the shower and that you have the required fault protection.
So in this case the rcbo is incorrectly sized for the final load 433.1.1 (i)
so i'm half right. the 40A MCB is running at above In, so is in danger of tripping if shower is used by teenage girls, which in this case, it is. 1 x 14 year old monster teenage daughter.
[automerge]1587049912[/automerge]
Apart from all that sounds like a good job.
just seen a pink pig in flight over the trees.
 
Last edited:

Reply to Report. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Planning on wiring my neighbour's summer house which will be 15 metres away from the end of the house (20-25 metres total distance from...
Replies
29
Views
7K
Hi. This is a gloriously messy installation I looked at this morning at a house a friend just purchased. It t became quickly clear it was more...
Replies
7
Views
1K
Hi all, This week while wiring a very old farmhouse for heaters I noticed the incoming cu tails were very long, around 20 metres from the fuse...
Replies
4
Views
2K
I suspect I know the answer to this already, but... For some reason, recently I've been getting increasingly ****** off by being undercut by...
Replies
11
Views
3K
Evening all.. I am currently doing my first full rewire. The customer is having the wall knocked down with the meter/cutout and CU on it. the...
Replies
75
Views
8K
Guest77
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock