M
masonc
I'm interested to see what cable would be used in the UK as the AC output cable from an SMA STP20000TL-EE inverter to the disconnect and panel. In the US, it would be #8 in conduit, but I like the multicore cable approach and I want to see if I can satisfy both BS and NEC standards.
The inverter Imax is 29A, under the NEC it would require a cable rated for at least 36.25A. Additionally, the cable has to be rated for outdoor applications.
Please let me know what is required under UK standards.
Chris Mason
Comet Solar
There are two requirements:
1) Current carrying capacity (See BS7671 depends upon type of cable and how installed)
and
2) Voltage Drop - once again BS7671 PLUS the PV design requirement of a voltage drop of less than 1% so that the inverters don't overvoltage.
So a 50kW system could be on anything from 25mm2 5 core SWA to 125mm2 4 core SWA depending upon the installation environment.
"25mm2 5 core SWA to 125mm2 4 core SWA"
So SWA would be normal? I would have thought that would be overkill for wiring the inverter to the AC Disconnect to the panel. What other cable is acceptable? I don't have a copy of
BS7671 (unless anyone can send me one).
all depends on the mounting method / cable run doesn't it.
this is one of those how long is a piece of string questions without the necessary information, but outdoor would mean not standard 4 core and earth, and tbh I just prefer to use SWA outdoors as it's going to be more durable, and the cost difference is minimal really in the grand scheme of a 20kW solar installation.