T
Toneyz
There was some published 16th ed. electrical theory books that had some tables in them based on cable size, protective device and incoming earthing arrangements etc by Trever E. Marks.
If 543.2.9 is the one about conductors in ting finals being connected end to end then that still allows for a lollipop circuit. It's just that the ring is fed from another length of cable. Apologies if I've misunderstood your post.
I don’t know about feared, but it was pointed out to me recently that lollipop circuits are not compliant. Reg 543.2.9 in the 18th. Not sure about previous editions to be honest.?

Not sure I agree with that .............
A lollipop circuit isn't a ring final circuit![]()
Hi Pete - sorry, but I stuffed up the naming conventions this morning, which both your-good-self and Lee are being very polite about, thanks !Wilko
Bit puzzled and not disagreeing in any way, but You mention R1+R2 for 100mts cable is less than 2 ohms.
Then in the next sentence r1+r2 is a bit less at 0.5 ohms both at 20degC.
It's probably me but can you explain what you mean ? sorry Mate just me wondering that's all.
I’ve recently had my scheme assessment - and my assessor was pretty adamant that the reg prevents lollipops. It’s certainly how it reads to me...
Take a demerit House point Wilko, see me after School every day for a week for Lines, and chastisementHi Pete - sorry, but I stuffed up the naming conventions this morning, which both your-good-self and Lee are being very polite about, thanks !
I'm back home now so I'll sit on the silly step for a while and drink my red medicine.



.Wilko, it's not something I would do, and I agree it's not a detailed departure from 7671, do you not think this interesting article, is a case of ELECSA interpreting things for their own interests? just saying. Would love to hear your educated comments please, it's just that I have very little trust in what the Schemes have to say, Spin Doctors, spring to mind.I too think lollipops are ok. Here's a little article from ElecSa on the topic for our evening reading.
Hybrid ring/radial final circuits - https://www.voltimum.co.uk/articles/hybrid-ringradial-final-circuits
Why would this type of circuit arrangement benefit any of the schemes for their own interest?Wilko, it's not something I would do, and I agree it's not a detailed departure from 7671, do you not think this interesting article, is a case of ELECSA interpreting things for their own interests? just saying. Would love to hear your educated comments please, it's just that I have very little trust in what the Schemes have to say, Spin Doctors, spring to mind.