I carried out a ring test and found it wasn`t a ring is there reason they cant be made into 2 x 20A radials.
find and verify the ends of each radial before giving each cable its own mcb.
simples
;-)
Just bung them on a 20A
If there is no continuity on the RFC then it has a fault that needs identifying and rectifying.
youre working on the assumption that 2 cables sharing an mcb must be a ring with absolutely no evidence to confirm this.