Wired an s plan recently and used the orange from each honeywell to send a switched live back to the boiler,after removing the link.Is this the best practise way,or should the greys and oranges of the valves be bridged across the control terminals of the boiler,as voltage free contacts?Thanks for any advice.
S
S
You should feed your external controls from LN & LS and return on LR. The boiler internal fuse needs to protect the control circuit. This is not the case in a lot of what I see however.
Which make of boiler has those terminals?
I am used to wiring Worcester Bosch boilers which have Ls and Ns for the supply to external controls and Lr for switched live, but other makes use other terminals.
A lot of combi's have just two terminals for external controls factory fitted with a link, some call them 1&2 others call them L & SL.
Dave,
Do,nt understand that,as the signal to fire the boiler comes from the s plan valves opening,not from the room stat and boiler stat.
Regards,S.
One of those terminals is the live out and the other the switched live back.
The live out is equivalent to the permanent live feed in a basic boiler cct.
So the live coming from the boiler will feed the programmer and the greys of the valves, the oranges of the valves will connect back to the other terminal.
Sorry Dave you are correct, Ls, Ns & Lr.
Ok, you were talking about Worcester too then.
My point is still that we don't know what make of boiler it is so don't know what terminals it has or what they are called.
Dave,Its a Baxi duotech,control terminals marked BK1 L in and BK2 L out.I can see your point about using internal boiler fuses for the external controls and may alter the wiring .
Regards,S
Read the boiler installation instructions to establish exactly how it should be connected. Which you should have done anyway before starting the job.
If they are like Worcester then the warranty may be voided the way you have connected it. And not compliant with bs7671 as not in accordance with manufacturers instructions.
Reply to s plan with combi boiler in the Central Heating Systems area at ElectriciansForums.net
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Hi all Mate of mine is getting a new utility room fitted, the kitchen fitting company have brought in their electricians for first fix and to be...
Hi chaps I’m wiring up a 2 zone heat system to a combi boiler. Do I need to replace the boiler mains cable with a 4 core cable and remove the link...