6
Evening all

Pricing up a consumer unit change in a large industrial unit

When it comes to selecting a 3Pole main switch for a 24 way distribution board, are there any factors that will change the decision between a 125A 3pole or 4pole main switch?
 
Evening all

Pricing up a consumer unit change in a large industrial unit

When it comes to selecting a 3Pole main switch for a 24 way distribution board, are there any factors that will change the decision between a 125A 3pole or 4pole main switch?
Yes is there a requirement to switch the N?
 
If a TT installation then provision must be provided to isolate all live conductors so a 4 pole switch would be required.
For TN installations where the Neutral is considered reasonably connected to earth by a low impedance,then 3 pole isolation is all that is required.
A removable link for the neutral for testing purposes is still required
 
Last edited:
It is easier for IR testing on a TN system to have a four pole main switch.
 
I have, rightly or wrongly always fitted a 3 pole switch, but most of my work is industrial and TN, you probably only have to worry about it on farms and other remote installations.
 
I alway fit 4 pole to make testing easier

It is easier for IR testing on a TN system to have a four pole main switch.

Is ease of testing really the most important consideration here? How much easier is it than dropping out the neutral test link and is that saving worth the potential risks?

If a four pole switch is used then it has the potential for the neutral contact to fail or not close in the correct sequence leading to a dangerous situation and significant damage to equipment. Far better to leave the neutral solid/unswitched wherever possible.
 
When it comes to selecting a 3Pole main switch for a 24 way distribution board, are there any factors that will change the decision between a 125A 3pole or 4pole main switch?

Yes, fit a 3 pole switch unless there is a specific requirement to fit a linked switch in the neutral.
 

Reply to Selecting a 3 or 4 pole main switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We are looking for a distribution board to provide 3 * 160A three-phase feeds, but they are basically redundant supply path options so max total...
Replies
4
Views
266
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
973
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K
I've been carrying out quite a few domestic extension first fixes recently which involves providing a power supply installed from the properties...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock