I could if it was 10 years earlier, but years go on and technology changes, maybe if you looked up UPs and VS companies, explain the scenario and conditions they will be able to advise you. That's what I did and got some good kit, it was used overseas in countries where the supplies weren't reliable, and had no trouble, the VS firm could also diagnose over the phone or by email, the UPs was EMERSON but that's all I remember, hope my reply has been useful, one thing the VS kit was dead simple to connect, loan and supply.Do you recommend any particular products??
One thing I did find with the UPs, if you are using any form of remote controls or sensing equipment, use a screened cable or twisted pairs to try and avoid voltage pick up, I had one install where the UPs was in a small room which needed to be Air Conditioned, ( it was in Asia so very hot) the customer required an emergency stop for the UPs, which involved a control pair, every time the AC started up out would go the UPs, took me a while to suss out that the control pair was picking up volts from the AC starting and tripped the UPs, worth noting, I think my detective work caused the supplier to add the proviso in their install manual. Clever git aint I?