That's standard SWA cable nothing special... lol!! Glad to hear your not TT'ing this shed now, especially as you have a TN-S earthing system. Just bury the cable deep enough not to be subject to future damage, or better still duct it...
 
mv x A x dist / 1000

For 4mm SWA at say 30A over 20m is 6.6Volt drop. or 2.87%

So 4mm SWA will be fine for your application.
 
I'd have sort of hoped he would have this down by now unless he was waiting for the spring weather ...........

But nice to calc it Helm
 