lionelmcc

I think the easiest and most cost effective way is to:

Check earthing arrangements and make sure they are up to regs.

Remove the RFC from the existing CU and install this into a separate 32A 30mA rcd enclosure.

Install 6mm from the spare way in the cu to feed this RCD. This will now RCD protect the circuit you will now spur off for the shed supply.

Install 13A sw spur and from this circuit somewhere convenient at the back of the house, run 1.5 SWA to the shed and install your light etc

I've been thinking about this and I might have to explain to the customer that his old fridge and freezer might both need replacing. and Also one more fridge on the existing kitchen ring.
Here is a suggestion, but I'm not sure whether this would comply with the regs;

fused spur from RFC in 1.5 SWA then radial in shed with visible wiring firstly to labeled freezer socket then to socket with built in RCD for general use, with light on 5a FCU from the same radial

Comments please
 
Sounds fine, however, the regs now say that ANY circuit that is extended, especially RFC, should have 30mA protection, which would negate the need for RCD protection in the shed.

Repeating myself here, socket outlets should be RCD protected anyway.

Gotta be honest, regardless of minor technicalities, i would not be happy doing the above.

Its my name on the cert at the end of the day.
 

Reply to shed revisited in the Australia area at ElectriciansForums.net

Similar Threads

Hi guys, I have supplied my Shed with a 6mm SWA cable into a nice consumer unit. In there I have a 6Amp MCB for the lights and a 16 A supplying a...
Replies
25
Views
894
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
537
Helping out a friend and a CU change is really the best option as sockets in kitchen and downstairs room not on RCD protection. Now one of the WTF...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock