A customer is wanting his shed wired. There is a 1.5mm hituf cable in the garden which was left for garden lighting. The customer no longer wants garden lights and was wanting me to use this 1.5mm hituf cable to run to the shed. It will need joined to extend it to the shed. The length of run from the house to the shed would be around 20meters.
He wants
4 tubular heaters: 120W each
1 indoor light: 28W
3 outdoor lights: 50W each
2 double sockets for tv/hifi
After doing calculations it seems that the 1.5mm hituf would be fine if I use a 10a breaker. The cable will be protected by an rcd.
I would much prefer to run a new cable to the shed and put a sub board in, but this would mean either digging up the tarmac or having the cable run overhead, which the customer doesn't want.
What are your thoughts?
He wants
4 tubular heaters: 120W each
1 indoor light: 28W
3 outdoor lights: 50W each
2 double sockets for tv/hifi
After doing calculations it seems that the 1.5mm hituf would be fine if I use a 10a breaker. The cable will be protected by an rcd.
I would much prefer to run a new cable to the shed and put a sub board in, but this would mean either digging up the tarmac or having the cable run overhead, which the customer doesn't want.
What are your thoughts?