A customer is wanting his shed wired. There is a 1.5mm hituf cable in the garden which was left for garden lighting. The customer no longer wants garden lights and was wanting me to use this 1.5mm hituf cable to run to the shed. It will need joined to extend it to the shed. The length of run from the house to the shed would be around 20meters.

He wants
4 tubular heaters: 120W each
1 indoor light: 28W
3 outdoor lights: 50W each
2 double sockets for tv/hifi

After doing calculations it seems that the 1.5mm hituf would be fine if I use a 10a breaker. The cable will be protected by an rcd.

I would much prefer to run a new cable to the shed and put a sub board in, but this would mean either digging up the tarmac or having the cable run overhead, which the customer doesn't want.

What are your thoughts?
 
my thoughts are that the 10A MCB will constantly trip and some numpty will fit a 32A, so the 1.5mm will melt. terll the tight-arse to get digging and the you can install a 6mm SWA with, as you said, a sub-main board.
 
I ran it by my supervisor and he said put a 10a mcb in for the meantime and if/when it trips then that's when we should tell the customer that we need to upgrade to a bigger csa.

About 2kw would you say and then pop?
 
A customer is wanting his shed wired. There is a 1.5mm hituf cable in the garden which was left for garden lighting. The customer no longer wants garden lights and was wanting me to use this 1.5mm hituf cable to run to the shed. It will need joined to extend it to the shed. The length of run from the house to the shed would be around 20meters.

He wants
4 tubular heaters: 120W each
1 indoor light: 28W
3 outdoor lights: 50W each
2 double sockets for tv/hifi

After doing calculations it seems that the 1.5mm hituf would be fine if I use a 10a breaker. The cable will be protected by an rcd.

I would much prefer to run a new cable to the shed and put a sub board in, but this would mean either digging up the tarmac or having the cable run overhead, which the customer doesn't want.

What are your thoughts?
Not enough heating when its cold, so they plug in a 3KW fan heater.....
 
I ran it by my supervisor and he said put a 10a mcb in for the meantime and if/when it trips then that's when we should tell the customer that we need to upgrade to a bigger csa.

About 2kw would you say and then pop?

10A MCB will run for about 1 hour or so at 3kW. about the limit for 1.5mm.
 
Yep get that 1.5 out of there! I ran a 4mm swa to my old shed years ago and then i replaced the shed with a 30x15 workshop, it needs at least a 10mm really for power requirements and to run the bonding back to the met! I'll get round to it one day!
 
I know Murdoch, I can see the problems already! What do you do with an awkward customer! Lol.
 
I know it's not an ideal situation and bad practice, but the current carrying capacity of the cable would be sufficient for the demand and the mcb shouldn't trip unless, as Murdoch says some one plugs a fan heater in. Am I correct in saying this?
 
spot on. do it right or let them get dodgy dave from the pub.
 
He wants
4 tubular heaters: 120W each
1 indoor light: 28W
3 outdoor lights: 50W each
2 double sockets for tv/hifi I'm giving that 1000W

If those numbers are correct, it only comes in at about 7 Amps!

Am I missing something here?
 
I have literally just installed 4 tubular dimplex 120w heaters in a room about 6ft x 6ft... The room doesn't heat up. Bad idea.