If you find a short circuit on the first leg of a ring final circuit between the consumer unit and the first socket, and the cable is buried. Can you pinpoint where the fault is? Also what would be the least destructive way to rectify the fault? Thanks in advance.
 
If your ohmmeter has a resolution of 1mΩ, you could measure the Line/Neutral loop resistance at the CU and work out the distance to the short circuit. (Table I1 in OSG)
 
If you've got a two part tracer (tx and rx units) then yes, potentially.
 