What about the ones marked up 230v ???
Can i ask why you chose SY ... its often misused and incorrectly installed and over the last 5yrs ive ripped out so much of this crap.. its design as a control cable the braid is a screening and is not mechanical protection, the outer clear sheath is unsuitable for outdoor use and whenever its is utilised as a power cable for LV the braiding should be earthed but a must is that it isn't used for earth.... not saying you have done any of this but interested to why this cable was chosen as i cant see any benefits with using it?