Biff. plain concentric can NOT be used after the DNO cutout!Under any circumstances!

Split concentric on the other hand can be when the proper regard to protection is observed.
well i would`v thought this was common sense Tony as well....
i mean is TN-C allowed in the UK for consumer install?....er..NO!!
 
I've been asked to wire a shed the customer said that he has got the cable when I looked at the cable it was single core like pme cable I guess the neutral and earth are both in the armoured sheath has anyone used this cable before?

There is no armouring on this cable, the concentric wires are the actual neutral and earth conductors. This cable is fine for the DNO's as the terminations and spreading of the conductors are hidden within the cut-out. It's a different matter for termination into standard electrical components (CU's/DB's and the like), and unless you know what your doing, can very easily end up looking like an amateurish pigs ear of a job!! The best and easiest solution is using a 3 leg heat shrink breakout and heat shrink tubing for the gathered concentric conductors.

The only way i would ever use this type of cable for underground installations, is within a heavy duty (thick walled) PVC duct, buried at a suitable depth. Which by the sounds of it, is what your going to have to do, if your going to use the customers cable!! Never install this type of cable in a direct buried situation.... Apart from anything else, it won't conform to the requirements BS7671...
 
There is no armouring on this cable, the concentric wires are the actual neutral and earth conductors. This cable is fine for the DNO's as the terminations and spreading of the conductors are hidden within the cut-out. It's a different matter for termination into standard electrical components (CU's/DB's and the like), and unless you know what your doing, can very easily end up looking like an amateurish pigs ear of a job!! The best and easiest solution is using a 3 leg heat shrink breakout and heat shrink tubing for the gathered concentric conductors.

The only way i would ever use this type of cable for underground installations, is within a heavy duty (thick walled) PVC duct, buried at a suitable depth. Which by the sounds of it, is what your going to have to do, if your going to use the customers cable!! Never install this type of cable in a direct buried situation.... Apart from anything else, it won't conform to the requirements BS7671...
and i`v heard of this going on in the past eng....this type of cable buried direct....
as I have already pointed out its commonly used in ducted risers (for flats and the like) ...but i`v heard of it being substituted for SWA....in a completely impractial and non-compliant fashion...
 
The outer serving on DNO concentric cable is a tough as old boots. It will take a lot more that a spade to break through it.

I acquired some to have a experiment with.
 
Biff. plain concentric can NOT be used after the DNO cutout!Under any circumstances!

Split concentric on the other hand can be when the proper regard to protection is observed.

my bad , pardon monsieur.
 
quote_icon.png
Originally Posted by driverman
There is a large electrical contracting company in my area that uses split concentric cable for sub - main cable between the DNO's OMB and consumer units when distance is more than 3 mtrs. They have been doing it for years. Easier to install than SWA cable.



Are the DNO happy with this? I only ask as EDF specify 25mm SWA?

Yes.......I worked for EON @ the time now WPD. I was surprised myself but all Ok with the DNO.

Sorry, that was my reply to a question by Phoenix
 