Ell181

DIY
May 10, 2025
3
0
1
cheshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)
So, a single phase motor I have bought. I have wired it up, as the diagram shows on the motor, and it's tripping the RCD when I turn it on. I have tried it wired up for forward and reverse and trips the RCD on both. I removed the lead that goes from the wall plug socket to the motor and tried that lead with a hair dryer - doesn't trip the RCD. So it must be the motor that is the issue.

I bought it from a guy who said it had been in a container for years - it looked unused since it still had the plastic cap on the shaft.

Here are pics of the motor, the way I wired it etc.
 

Attachments

  • a8a40fd3-8362-4621-a6f3-19ccdfcd1e56 (1).jpg
    a8a40fd3-8362-4621-a6f3-19ccdfcd1e56 (1).jpg
    97.5 KB · Views: 63
  • b15a35df-658b-43de-94dc-1332c33da3a0.jpg
    b15a35df-658b-43de-94dc-1332c33da3a0.jpg
    134 KB · Views: 51
  • 1529edc0-cda8-4110-b0f9-7e271f7ccaa2.jpg
    1529edc0-cda8-4110-b0f9-7e271f7ccaa2.jpg
    147.4 KB · Views: 55
  • e366d0ee-729e-4b14-91a6-1a1b50b52eb7.jpg
    e366d0ee-729e-4b14-91a6-1a1b50b52eb7.jpg
    166.6 KB · Views: 50
  • 129e33ed-b39f-4847-83e8-fdf483025b43.jpg
    129e33ed-b39f-4847-83e8-fdf483025b43.jpg
    154.4 KB · Views: 56
  • 63544a67-8122-46cb-9779-02a4da28e0ab.jpg
    63544a67-8122-46cb-9779-02a4da28e0ab.jpg
    139.5 KB · Views: 53
I would insulation test the windings and capacitor
If you don’t have the equipment to do that, put it in a warm dry place for a week with the cover off.

I would replace the capacitor if it has been standing for years, they can dry out and fail with a bang!
 
  • Like
Reactions: Ell181
I would insulation test the windings and capacitor
If you don’t have the equipment to do that, put it in a warm dry place for a week with the cover off.

I would replace the capacitor if it has been standing for years, they can dry out and fail with a bang!
I opened up the motor and the windings in the stator were black, has to be burnt out for some reason.
stator.jpg
 
Last edited by a moderator:
Looks like it has been left powered with the shaft held stationary
Only cooked the windings in 2 opposite positions
 
I opened up the motor and the windings in the stator were black, has to be burnt out for some reason.
Throw it in the scrap bin.
 
  • Like
Reactions: Ell181
Throw it in the scrap bin.
Told the seller and got a refund. Kept the starter capacitor though - do you think the capacitor might be in bad way as well?
 
  • Like
Reactions: James
There's a good chance that a failing capacitor was the root cause of the winding failure.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
cheshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Single phase motor tripping RCD
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Thread Tags

Advert

Thread statistics

Created
Ell181,
Last reply from
brianmoooore,
Replies
7
Views
406

Advert