In an industrial building with galvanised trunking everywhere and loads of circuits with singles, has anyone got any good tips on identifying the singles for a circuit easily if I needed to break into a ring for example?
 
Just have to disconnect legs from socket and pull in new leg.

The whole point of trunking and conduit is that it’s rewirable.
There should be no need for joints inside trunking.
 
we used to tape each circuit cables together every 4ft. - 6ft.
 
I would rarely cut into a single cable within the trunking system unless it were an emergency fix

As already mentioned You should find the nearest point and pull in a new cable length

Quite a few times I come across trunking absolutely bursting with cables which you can barely get the lid on which in this case you might want to run in some new containment if the budget allows
 
Go to the nearest socket where you want to break in follow the singles into the trunking, best to make you connections in socket not in the trunking, you could clamp both LN under load an compare as mentioned but dont think its necessary I would not.
 
Go to the nearest socket where you want to break in follow the singles into the trunking, best to make you connections in socket not in the trunking, you could clamp both LN under load an compare as mentioned but dont think its necessary I would not.
Apologies the alcohol talking again
 

Reply to Singles in trunking in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have checked the regs and can't find anything to say this can't be done. Although I'm worried about cable movement in the case of short circuit...
Replies
43
Views
2K
Since the deco needs doing to this property. My sister needs the TV putting on thr wall but wants the cables hiding. What will be the best way...
Replies
4
Views
335
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
So I'm starting out a new rig and I'm fresh out of college with my level 3 without any experience and I think that I need to still have the...
Replies
5
Views
674
Is anyone aware of any galv trunking that is smaller than 50x50. I'm drawing a blank online. I've taken over a job that's used 16mm twin and earth...
Replies
12
Views
778

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock