Thanks guys.
Sounds like kinda what I suspected. I am going to try to get a better look at the stuff on the ground floor and take what covers off i can and hopefully I should see the cable shield earthing arrangement there attached to the the conduit that leads to the metal box in the flat.
I guess if I have continuity from there to the metal box in the flat then I am all good and do not need to see an actual earth cable from the supply or get a specific one run to this installation. From what i remember the regs says something about "suppliers conduits and equipment being a valid earth from supply" will need to look it up tonight.
After sorting through the mess the cable condition were better than I expected. IR was fine >299 megohms on all circuit. But i am rewiring 4 of the 6 circuits including the lights as there was no CPC
. A lot more work that I was originally expecting but thats how it goes sometimes
Thanks again guys
for helping out a newb .
Sounds like kinda what I suspected. I am going to try to get a better look at the stuff on the ground floor and take what covers off i can and hopefully I should see the cable shield earthing arrangement there attached to the the conduit that leads to the metal box in the flat.
I guess if I have continuity from there to the metal box in the flat then I am all good and do not need to see an actual earth cable from the supply or get a specific one run to this installation. From what i remember the regs says something about "suppliers conduits and equipment being a valid earth from supply" will need to look it up tonight.
After sorting through the mess the cable condition were better than I expected. IR was fine >299 megohms on all circuit. But i am rewiring 4 of the 6 circuits including the lights as there was no CPC
. A lot more work that I was originally expecting but thats how it goes sometimes Thanks again guys
for helping out a newb .