A

ashlec

Hi, ive recently went to look at a job where the customer had a condition report done on a v-small ind unit & 1 of the faults was mentioned was no RCD protection to a 16a outside socket for the local snackvan, now my question is can a 16a commando socket be installed on a 32a ring when its supplying a 2way garage d/b with a 40A 30ma RCD main switch, 16a radial for skts ( kettle/ toaster/ coffee machine & tea urn etc)& 6a for lighting ( 6ft flo )? Surely this COULD potentially exceed the 16a rating of the o/s commando socket ?

The company that done the test just suggested that they were going to replace the MCB's for RCBO's & wanted silly money for doing it hence me getting involved....and they seemed to ignored the fact that there were knockouts missing in the D/B where you could poke both fingers through, i have my doubts about them....

looking forward to hearing your inputs.
 
IMO, the socket should be RCD protected , then the hook-up lead is protected. problem then is you will have 2 30mA RCDs in seies in the snak van, so no discrimination. look forward to hearing other members ideas on a possible solution.
 
You don't mention that type, size and length of cable is connected to the commando socket.
Are you saying that the cable is spured off a 32a ring with no additional fusing?
 
Simpler to place the protection at the supply end and remove the snack bar CU RCD, replace it, with a standard DP switch!! Not going to be much of a problem either way, as this industrial unit has been described as Very small, so not that far to switch back on again..!! lol!!

Sounds like you could ideally do with a 32A socket outlet, on it's own circuit, rather than a 16A spur off a ring circuit!! Do a clamp test at the snack van CU to see what it's actually pulling in worst case scenario..
 
IMO, the socket should be RCD protected , then the hook-up lead is protected. problem then is you will have 2 30mA RCDs in seies in the snak van, so no discrimination. look forward to hearing other members ideas on a possible solution.

It's a general problem that. No real getting around it because i agree the hook-up should be RCD protected. The discrimination issue, i always note on the test sheet (so that anybody else with half a brain cell knows im aware of the issue) No other real way of getting around it, unless you do as E54 says and dp switch the upstream - only issue with this is then they'll have to go outside to switch it back on if it trips off, and most customers will like to voice there opinion on that, especially if its cold outside lol.

There is potentially the posibilty of overload. - although it's slim. Only real option i can see is de-rate the outside breaker to a 16 to match the commando socket, then if you do start to pull more than the intended 16A it'll just trip out.

I mean if the snackvan was never going to be moved the easy option on the overload issue would be to bypass the commando socket, select a suitable cable size and hard-wire it.

Just really means that they have to go outside all the time to reset
 
No other real way of getting around it, unless you do as E54 says and dp switch the upstream - only issue with this is then they'll have to go outside to switch it back on if it trips off, and most customers will like to voice there opinion on that, especially if its cold outside lol.

The chances are that you have to go outside anyway, as in all liklihood both RCD's will be taken out of service on a fault!!
 
You don't mention that type, size and length of cable is connected to the commando socket.
Are you saying that the cable is spured off a 32a ring with no additional fusing?
The size of the cable is no greater than 2.5mm flex, length is about 15-20 metres, the 16amp socket is connected directly on to the ring & not fused down. My concern is the socket could potentially pull more than the 16a rating. Im thinking a 16A 30ma rcd connected fitted inside before the o/s socket ?
 